-   -   GFCI question regarding hardwired vs plug-in disposal (http://www.diychatroom.com/f18/gfci-question-regarding-hardwired-vs-plug-disposal-139671/)
mystic_cobra 04-08-2012 02:25 PM
My old garbage disposal was hardwired to its own 15A non-GFCI circuit using a cable coming straight out the wall. After renovation the entire kitchen, we decided to switch to a countertop button with the air/vacuum type switch. Now I'm using a plug in cord and a std outlet/receptacle that I installed under the sink. Should this be a GFCI outlet?
1965 house, Northern VA
thanks
Jimmy
gregzoll 04-08-2012 02:27 PM
It is up to your local regulations to decide that or not. If you want to feel safer, go ahead and install a gfci outlet under there.
Speedy Petey 04-08-2012 02:32 PM
Regardless of how it is wired, it does not need a GFI.
Put one in if you like, but it is not required.
electures 04-12-2012 09:48 PM
GFI is not required.
mystic_cobra 04-12-2012 10:33 PM
Thanks guys. I guess it makes sense. Not much chance of a garbage disposal falling into a sink full of water while someone is washing dishes. :laughing:
k_buz 04-12-2012 10:38 PM
Actually, it doesn't make much sense at all...but per the code, you don't need to install a GFI under a sink.
mystic_cobra 04-12-2012 10:46 PM
I guess you could have an internal short inside the disposal or something, right?
If you guys were installing one of these in your own kitchen would you install a GFCI?
gregzoll 04-12-2012 10:47 PM
Not, due to not required either on the Disposal, Dish washer, Trash Compactor, Stove, Fridge. Only needed on the countertops.
k_buz 04-12-2012 10:48 PM
No I wouldn't. I just don't understand the thinking behind some of the codes, and this is one.
k_buz 04-12-2012 10:50 PM
That's not true. If an outlet is within 6' of a sink, it needs to be GFI protected. But the disposal and dishwasher doesn't count because they consider the outlet to be protected by a physical barrier...which is either the countertop, or the sink itself...while ignoring all the plumbing under the sink.
Speedy Petey 04-13-2012 06:37 AM
I don't understand the logic behind this.
How is this ANY different from having wiring or device boxes in stud bays with plumbing? Or having a panel next to a slop sink? Or having a hard wired septic pump?
NONE of which are inherently unsafe, nor would benefit from GFI protection.
Speedy Petey 04-13-2012 06:39 AM
GFI protection has nothing to do with short circuit protection. That is what the circuit breaker is for.
Contrary to what many/most people think, a GFI is NOT a circuit breaker.
I didn't in mine, and don't for customers either.
gregzoll 04-13-2012 08:17 AM
May want to go back and read what I posted, then go and read the NEC regarding Where they are and are not required in a Kitchen. I do believe that I covered that under the word "Counter tops". When have you seen a gfci outlet or protected outlet on a baseboard in a Kitchen?
electures 04-13-2012 09:12 AM
No. Because it is not required.
itsnotrequired 04-13-2012 11:04 AM
i thought the 6' sink rule only applied to sinks NOT in a kitchen. by default, all the receptacles serving countertops in a kitchen need to be GFCI so anything by a kitchen sink would be GFCI anyway. the receptacle under the sink for a disposal is not installed to serve countertop surfaces and thus does not need to be GFCI protected.
but this brings up an interesting question: say i have a wet-bar sink with a disposal and a receptacle under the sink to serve that disposal. would that need to be GFCI? it would be within 6' of the sink but 'protected' by the countertop, cabinet door, etc. i mean, if the wet-bar was in the middle of a room with a wall behind it, a receptacle on the other side of the wall wouldn't need to be GFCI. i'm thinking the disposal receptacle would not need to be GFCI.