Old 04-16-2009, 04:55 PM   #31
nap
You talking to me?
nap's Avatar
GFCI question: can line and load wires be run inside the same conduit?
Originally Posted by wildcat View Post
This is how it was explained to me in school. You want the over current protection to be the weak link in the circuit, so you want the breaker to trip before the wire gets anywhere near being overloaded/overheating.
So in this case you're derating the wire which could cause the wire size to increase so that the amp rating of the wire remains greater than the load at which the breaker will trip.
Boy, building electrical design seems soo long ago for this structural engineer.
what?
You derate the wire (when running multiple wires in a conduit) due to the heat buildup, which causes increased resistance which causes voltage drop and on in circles.
You use a lower amperage breaker so you do not draw as much current through the wire to cause a heat buildup.
Heat is bad.
I'm not really sure what you said.
Old 04-16-2009, 05:36 PM   #32
Chicago, IL
Michael Thomas's Avatar
It's not surprising that many people find this confusing, the difference between maximum OCPD requirements and maximum conductor ampacity is often not clear, even in manufacturer's specs (!), for example:
Michael Thomas is offline   Reply With Quote
Old 04-16-2009, 07:07 PM   #33
Bigplanz's Avatar
First, thanks everyone for your helpful and insightful answers. I have learned a lot from this thread. That's always fun!
I believe I was mistaken, and that the derating is indeed taken from the ampacity table in it's original form. The NEC says this:
240.4(D) Small Conductors. Unless specifically permitted in
240.4(E) through (G), the overcurrent protection shall not
exceed the following after any correction factors for ambient
temperature and number of conductors have been applied.
The required amperage over protection (15 amps in this instance) is calculated AFTER derating for temperature and number of conductors.
One other thing I found is:
110.14 (C) Temperature Limitations. The temperature rating associated
with the ampacity of a conductor shall be selected
and coordinated so as not to exceed the lowest temperature
rating of any connected termination, conductor, or device.
Conductors with temperature ratings higher than specified
for terminations shall be permitted to be used for ampacity
adjustment, correction, or both.
This indicates to me that if you have a mixed system, with some conductors/terminals rated at 60 degrees C, and others at 90 degree C, then you derate from the lowest temperature conductor/terminal in the circuit. In this instance, 14AWG wire at 60 degree C would still work, in that it is rated 20A and a 80% derating would still put it at 16A, within the range of the breaker's coverage.
Thanks for the interesting discussion. This has been one of my favorite threads in awhile.
Oh, I found out Kentucky is still on the 2005 NEC and that local jurisdictions have to use it, as it is a state-wide regulation.
http://www.iaei.org/directconnect/states/KY.html
Bigplanz is offline   Reply With Quote
How to wire to GFCI's with one line? gante Electrical 8 03-15-2009 12:30 AM
Bathroom circuit: 60V between line and load? Niels Electrical 4 11-30-2008 05:00 AM
GFCI Trips campbellpt Electrical 28 11-21-2008 04:06 PM
GFCI in detached garage question WShawn Electrical 2 08-02-2008 04:27 PM
Load vs. line wire gvernea Electrical 5 01-16-2008 01:50 AM