Old 02-06-2013, 07:44 PM   #1
gfci question
I was testing a portable gfci cord and found that it would shut off with the test button and reset normally with the reset button. Next I tested it with my gfci outlet tester and it would not shut off. Is the gfci good or bad???
Reading on line it appears that separate outlet testers will not work on a two wire ungrounded system. This is a three wire (grd-blk-wht) set up. The gfci has a 10mA trip current. It appears that most Gfci's are in the 4-6 mA range.
Could it be that the outlet tester is a lower current trip rating than the 10mA and that is why it will not trip the gfci???
bottom line is the pigtail gfci any good?
thanks for any input and thoughts.
bernie
bernie963 is offline   Reply With Quote
Old 02-06-2013, 10:09 PM   #2
gfci question
Outboard testers operate by sending some current down the ground wire. If the ground isn't connected then such a tester won't work. This doesn't mean the GFCI is faulty, its just the outboard tester can't create a leakage (fault) current without a ground. So it isn't anything to do with how much of a leakage current the outboard simulator makes vs. the internal GFCI test button. Without a ground return the outboard tester leakage is zero mA.
The test button on the GFCI device works differently, it sends a return current back down the neutral but it sends that current return outside of the differential transformer inside the GFCI. This creates a current imbalance which trips the GFCI. This is why the GFCIs test switch can work without a ground line.
curiousB is offline   Reply With Quote
Old 02-06-2013, 11:12 PM   #3
Licensed Electrician
k_buz's Avatar
gfci question
According to the specs of every GFI outlet I've installed, the only way to test them is with the "Test" button on the device. I will bet that your GFI cord is the same. If you press the Test button and it trips, you can assume it is working.
Location...Location...Location
Old 02-08-2013, 04:14 AM   #4
gfci question
Thanks guys. Yesterday I spoke with an electrician (co-worker) about gfci testing. He suggested that the older gfci's may and do fail to operate correctly even if the test button works. The newer ones don't fail with age. Older styles have to be exersized monthly or the contacts weld together.
Also different testers do have different mA leakage which is why some gfci;s will not trip on an external test.
His advise, throw it away, better safe than sorry.
On a totally different note: K_buz, you mentioned on another thread about cordless vs corded drills and using extention cords "that they come in different lengths" I am being polite by posting this here. You missed the obvious, "they also come in different colors" HA, HA
bernie
Old 02-08-2013, 06:22 AM   #5
gfci question
Your electrician friend is wrong. This is nothing to do with GFCI sensitivity. I outlined the exact issue two posts prior.
Old 02-08-2013, 06:52 AM   #6
gfci question
GFCI devices do not use a ground wire in the test or fault mode. GFCI devices will/should work fine without a ground present.
danpik is offline   Reply With Quote
Old 02-08-2013, 10:45 AM   #7
gfci question
Of course. I outlined this above. An external GFCI tester will not work without a ground.
GFCI question regarding hardwired vs plug-in disposal mystic_cobra Electrical 24 04-13-2012 07:26 PM
GFCI outlet and breaker question danette32 Electrical 5 02-11-2012 06:25 PM
GFCI Conduit question llenod Electrical 3 04-06-2011 01:09 PM
GFCI question. Please Help. the banana k1ng Electrical 4 10-09-2009 08:35 PM
GFCI Question Mdbuilder Electrical 6 06-19-2008 04:15 PM