-   -   GFCI protection of bathroom (http://www.diychatroom.com/f18/gfci-protection-bathroom-156421/)
zubor 09-10-2012 03:49 PM
I have a bathroom circuit I need to GFCI protect.
Power comes from the panel to a receptacle just outside the bathroom. From the receptacle to two switch boxes - one which controls a light outside the bathroom door - and one to a switch box in the bathroom. From the switch box in the bathroom to a light, a fan, and a receptacle beside the sink.
The switch in the bathroom is within 1 m of the shower stall so needs class A GFCI protection and the receptacle beside the sink needs GFCI protection.
Two questions:
1. Is it allowed to protect the whole circuit by replacing the first receptacle with a GFCI receptacle and connecting lines an loads appropriately?
2. This first receptacle supplied two other enclosures. Can I bring power in, tie it into the line screws, and pigtail the two loads before connecting to the load screws?
The box is 18 cu.
A $20 GFCI receptacle is much more attractive than an $85 GFCI breaker :)
Gac66610 09-10-2012 05:57 PM
The switch, outside the shower does not need protection, unless it switches a fan in the shower. The receptacle does need to be GFCI
kevinp22 09-10-2012 07:12 PM
didnt notice Canada location. post deleted
Gac66610 09-10-2012 07:31 PM
Originally Posted by kevinp22 (Post 1007147)
Code for renov/new requires bath only loads on bath rec circuits, but i assume just replacing a device wouldnt trigger requirements to update???
Local rules vary, I would assume no ... but you know what they say about assuming, check with local building division.
jbfan 09-10-2012 08:29 PM
By him using 1 m of the shower makes me think he may be in Canada, so US rules would not apply.
zubor 09-10-2012 08:48 PM
Yepp. I'm in Canada. According to the CEC, all switches within 1 m of a shower stall must be GFCI class A protected.
From ESA FAQ:
Question
Is a separate circuit required to supply a receptacle in a bathroom?
Answer
The code does not require a separate circuit for bathroom receptacles. Bathroom receptacles can be supplied by a general purpose circuit that supplies other general purpose receptacle and lighting outlets. Multiple bath and washrooms are permitted to be supplied by the same circuit.
Gac66610 09-10-2012 08:55 PM
ummmm oops, didn't even notice:whistling2: