Old 03-04-2012, 10:56 PM   #1
GFCI to protect pool light
I currently have a two gang box that has a gfi and a switch to control my pool light.
The pool light is getting power from the "line" side of the gfi and is not protected.
I installed a new gfi and hooked the light to the load side and everytime I switched on the light it trips the gfi, what should i do to correct this?
Thanks in advance!
serrano is offline   Reply With Quote
Old 03-04-2012, 11:06 PM   #2
Electrical Contractor
kbsparky's Avatar
Replace the light. Obviously it is leaking current into the pool ....
-KB
Old 03-04-2012, 11:09 PM   #3
So it sounds like i hooked it up correctly I assume?
Old 03-04-2012, 11:14 PM   #4
retired elect/hvac/plumb
plummen's Avatar
Drain the pool and check the light fixture would be a good starting point safety wise anyway
"facts" have no relevance to this discusion
Posting from a concrete bunker under a non descript barn
plummen is offline   Reply With Quote
Old 03-04-2012, 11:15 PM   #5
Thanks guys!
Old 03-05-2012, 07:17 PM   #6
If the pool light is an old line-voltage type, you might want to consider replacing it with either a low-voltage type, or a fiber optic unit that has the light source away from the water. Those old line-voltage lights always leaked some current. When the NEC first called for GFCIs in the 1970s, it had a special rule for a special type of GFCI that allowed more leakage current, for use with pool equipment. That exception went away in, I think, 1987.
fa_f3_20 is offline   Reply With Quote
GFCI with 2 light switches in same box civdtm Electrical 2 10-18-2011 06:45 PM
GFCI Breaker Trips when any light is turned on rexnance Electrical 3 06-03-2011 10:55 AM
GFCI for the Lamp Post (GFCI for circuit that is fed Power from light) jamiedolan Electrical 7 02-25-2009 11:50 PM
Replace pool light DONRILEY Electrical 5 07-20-2008 05:51 PM
Can a GFCI protected light be installed into a normal light circuit? boongywoongy Electrical 6 05-19-2008 09:02 PM