Hi,
I'm in the process of installing a 15 amp GFCI outlet in the kitchen and noticed the following:
The oulet has a red(hot), black(hot) and white(neutral) wire. At the panel this is connected to two 15 amp breakers. It looks like it running to two seperate outlets. It is possible to connect a GFCI to this outlet? or is better to install a GFCI breaker at the panel? Any suggestions or recommendations is greatly appreciated.
anthony9887 is offline   Reply With Quote
Old 12-02-2008, 08:14 AM   #2
Where is this outlet located and what is it used for?
What is wrong with the existing outlet?
Why are you installing a GFCI at this location?
Billy_Bob is offline   Reply With Quote
Old 12-02-2008, 08:19 AM   #3
Licensed Pro
Originally Posted by anthony9887 View Post
Hi,
Sounds like a split kitchen receptacle in Canada. No, a GFCI receptacle will not work here. You will need to use a double pole GFCI breaker instead.
Old 12-02-2008, 08:31 AM   #4
Couldn't a GFCI be used if the circuit was branched off before the GFCI?
jerryh3 is offline   Reply With Quote
Old 12-02-2008, 08:37 AM   #5
joed's Avatar
Rewards Points: 12,852
If this is a kitchen counter circuit in Canada only three options. Use a double pole GFCI breaker or replace circuit with #12 wire and 20 amp T slot GFCI or leave as is. It is grandfathered and is not required to be changed.
Old 12-02-2008, 09:58 AM   #6
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
I would agree with leave it alone. The only way you can install a gfci receptacle would be if only one of the hot wires is terminated on the receptacle and the other passes through the receptacle box. What you have is a multiwire branch circuit sharing a single neutral.
If both red and black hot wires are terminated then your choices are as Joe and househelper said if you live in Canada. If you live in the US you may leave it alone as 15 amp kitchen counter receptacle branch circuits would have been installed in the 1980's and are grandfathered.. same in Canada. If the kitchen receptacles on this multiwire branch circuit do not have both hot wires terminated on them and you live in the US the two diagrams below show your options.
Old 12-02-2008, 10:06 AM   #7
The outlet is located in the kitchen. I wanted to upgrade the existing outlet to GFCI protection. House is only 15 years old and in Canada. Is it easy to install the double pole GFCI breaker or should I have a technician install it.
Thanks guys for you suggestions.
Old 12-02-2008, 10:19 AM   #8
Rewards Points: 2,350
Surely this wouldn't count as the two required circuits, would it? I mean, if it terminates into a split wired duplex and goes no further, and is the only thing on the circuit, that would mean the other receptacles in his kitchen would be on different circuits. Maybe this circuit was split wired for a couple of appliances that are no longer there.
Anyway, to the OP, is there only one receptacle in your kitchen, or what?
Old 12-02-2008, 10:22 AM   #9
UAW SKILLED TRADES
Stubbie's Avatar
I see we posted at the same time.... Yes the installation of a gfci is very simple. Biggest mistake people make is connecting the neutral of the branch circuit to the neutral bar....it must connect to the neutral terminal of the gfci and the white pigtail of the gfci then connects to the neutral bar of the panel. So you will need to trace the white neutral to the neutral bar remove it and connect it to the gfci. Turn your main breaker off just to be on the safe side when you install it.
Added note.... double pole gfci's are very expensive....
Old 12-02-2008, 10:25 AM   #10
UAW SKILLED TRADES
Stubbie's Avatar
Inphase
I'm understanding that there are two duplexes involved with this branch circuit.
Old 12-02-2008, 10:40 AM   #11
Originally Posted by Stubbie View Post
Inphase
I missed that part. There should be no reason then, that two GFCI receptacles wouldn't work. He just needs to re-wire the neutral at the first box into a pigtail, and pass one circuit through to the next GFCI. The shock he receives from the price of the GFCI breaker may be worse than the shock from not having GFCI protection!
Old 12-02-2008, 03:12 PM   #12
I thought about getting a double pole 20 amp gfi breaker for an indoor spa (plug in type), after seeing the prices...2 gfcis are the better choice.
rgsgww is offline   Reply With Quote
GFCI problem with pond pump sandsmarc Electrical 21 04-05-2013 12:51 PM
40 amp double pole gfci problem rivers Electrical 38 07-19-2008 12:10 PM
gfci problem - 120v between ground and neutral dave0419 Electrical 1 08-18-2007 12:01 AM
gfci problem farrington135 Electrical 1 11-15-2006 06:57 PM
GFCI problem Unregistered Electrical 3 02-08-2004 09:41 PM