GFCI Problem - Electrical - DIY Chatroom Home Improvement Forum
Old 02-27-2011, 02:41 PM   #1
Rewards Points: 113
GFCI problem
I just installed a GFCI in my kitchen. This outlet also fed an outlet in a room adjacent to the kitchen. I pigtailed off the hot and neutral and wired to my GFCI. Hot and neutral went to the line terminals and I did not use the load terminals. I plugged a lamp into it for test and the lamp would not work in the test and did work in the reset.
However, with the lamp unplugged and GFCI in the test mode, my tester indicates that both top and bottom hot receptacle slots of the GFCI are still hot. When I plug the lamp back in during the test mode, I get a short burst of phantom current in the other hot slot and my tester indicates no current in the line to the lamp. I checked the terminals and the black is to brass and neutral is to silver.
The bath GFCI I installed with line and load connections has no current to the hot receptacle slots when it is in test mode.
Any ideas as to what is going on? Why is there current in the hot slots when in test mode and nothing plugged in?
Captflx is offline   Reply With Quote
Old 02-27-2011, 03:18 PM   #2
Rewards Points: 113
GFCI problem
O.K., after posting, I tossed my "voltage detector" and used my voltage meter. It is reading less than a volt when ther GFCI is in test mode. Should this voltage be there? It is apparent the voltage detector is extremely sensitive.
Thanks.
Old 02-27-2011, 03:47 PM   #3
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Thanks.
Non contact testers (voltage detectors) are the wrong instrument to check a gfci for voltage when the gfci is tripped using the test button. Trip the gfci with the test button , there should not be voltage hot to neutral and nothing should operate if plugged into that gfci. Reset it and all should be well. Less than a volt on a multimeter is nothing to be concerned with.
As for testers it doesn't get much better than the fluke line of testers. My new favorite is the T-Plus for around the house for testing voltage and continuity. It won't read all that phantom voltage causing you great confusion.
Testing for current I have a few others I like.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 02-27-2011, 05:21 PM   #4
Rewards Points: 113
GFCI problem
Thanks Stubbie. Good advice. The detector is easy to use but I've just found out it's not the one to use in all situations.
Pond pumps tripping GFCI lendosky Electrical 23 12-23-2010 03:22 PM
20 amp GFCI breaker pops when pool pump is turned on. jagrunner Electrical 11 03-19-2010 04:31 PM
new gfci on new circuit pops rtoni Electrical 39 11-15-2008 10:18 AM
20 Amp Breaker tripping with GFCI panhandlion Electrical 7 12-12-2007 08:59 PM
GFCI problem Unregistered Electrical 3 02-08-2004 09:41 PM