Around my kitchen counters there are about 12 outlets but only one is a GFCI protected outlet. The breaker labeled "Kit. Rec." is not a GFCI protected breaker.
As long as the GFCI outlet is the first in line to the breaker then all of the outlets are protected??? Is this correct?
MisterSteve is offline   Reply With Quote
Old 03-03-2012, 10:10 AM   #2
Your Facilities Guy!
Not necessarily, it depends if the outlet is wired in series or in parallel. The outlets downstream from the must be feed from the appropriate terminal on the GFI most gfi breakers are labeled well if yours is not find a wire diagram online sand it should tell you the load and line terminals. Remember to wire through the outlet
Donnig is offline   Reply With Quote
Old 03-03-2012, 10:24 AM   #3
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,252
All receptacles are wired in parallel never in series. The GFCI has line terminals (power from breaker panel) and load terminals (used to GFCI protect down stream receptacles. To test to see if the other receptacles are protected, push the test button on the GFCI. The GFCI receptacel and properly wired down steam receptacles now should be dead. Test with a lamp. If any receptacles still work, they are not connected to the load terminals of that GFCI.
Coastal South Carolina
Old 03-03-2012, 10:24 AM   #4
Rewards Points: 330
from breaker to gfci is line side.load side goes to the rest of the outlets on that ckt.
oleguy74 is offline   Reply With Quote
Old 03-03-2012, 10:37 AM   #5
My next question is whether this same practice can be used for two separate bathrooms. Better way of wording this... Can TWO bathrooms with a total of 4 receptacles be on the same breaker and protected by one GFCI outlet. They are set up with the GFCI in 2nd bathroom feeding the three outlets in the master bathroom which has no GFCI's in it.
Old 03-03-2012, 10:46 AM   #6
A "Handy Husband"
rjniles's Avatar
Yes they can. But current code requires that if the circuit is shared by the receptacles in 2 baths, nothing else can be on that circuit. That means the lights or fans must not share that circuit.
I used to live in a house built in 1978 that the receptacles in 3 baths and 2 outside receptacles were on one GFCI breaker. No GFCI in the kitchen. Not sure that was code even then
Old 03-03-2012, 10:49 AM   #7
Thanks RJ
Old 03-03-2012, 11:32 AM   #8
Rewards Points: 3,256
That's the way my house is wired. When there is a wind blown rain storm sometimes my GFI trips.
zappa is offline   Reply With Quote
Old 03-03-2012, 12:08 PM   #9
A "Handy Husband"
rjniles's Avatar
Check the covers and gaskets on the outside receptacle covers, you are getting moisture into the receptacles or wiring.
Old 03-03-2012, 12:35 PM   #10
Electrician
SD515's Avatar
Rewards Points: 504
Check for nicks in the wiring also. I had outside recepts tripping the GFCI breaker during rain storms before I found and fixed them.
Kyle
GFCI Outlets in Series allbymyself Electrical 6 01-24-2011 11:52 PM
GFCI breakers equivalent to GFCI outlets? Any code pitfalls? TomServo Electrical 27 02-04-2010 10:59 PM
Replacing kitch outlets to GFCI jhubert Electrical 7 11-16-2009 07:23 PM
downstream of GFCI outlets amakarevic Electrical 11 12-25-2008 01:13 PM
two GFCI outlets at bath vanity Hickory Electrical 6 12-18-2005 09:31 AM