I just installed a new GFCI outlet to the exterior of my house. I ran the power from a switch inside the house. When i test the outlet with my voltage tester it blinks red indicating power...I plugged in a lamp and it did not turn on. I tried plugging in other items as well, with no luck. I'm very confused as to how this outlet is not working properly. I only have wires going in to the load part of the outlet, coming from the switch inside. There are three other switches in the same box, 2 of which are used to power the outside outlet. Please help!
-Stuart
Stmorris987 is offline   Reply With Quote
Old 12-03-2012, 10:32 AM   #2
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,180
You may have connected to a switch loop and/or there is no neutral in the box. Show us a picture of the box with the switches pulled out (not disconnected).
Coastal South Carolina
Old 12-03-2012, 10:43 AM   #3
Electrical Contractor
jbfan's Avatar
Rewards Points: 384
The power to a gfci is connected to the line and not the load.
Old 12-03-2012, 10:49 AM   #4
A "Handy Husband"
rjniles's Avatar
Missed that!
Old 12-03-2012, 11:38 AM   #5
So, I don't know why i said "load", I meant to say the wires are going in to the lead. When I test the outlet with nothing plugged in, it reads hot, but when I try plugging in the lamp, the outlet reads cold.
here's a picture of the inside box, hope it helps...
Old 12-03-2012, 01:08 PM   #6
jbfan's Avatar
Rewards Points: 384
You have 2 switches that power the same receptacle?
Old 12-03-2012, 02:33 PM   #7
I'm drawing power from one switch (which controls an outside light) to a new switch that controls the outside outlet (i really just installed this so i could put up christmas lights and turn them on/off)...I feel like there is an issue with the ground wire?? I can't depress the reset button...
Old 12-03-2012, 02:42 PM   #8
jbfan's Avatar
Rewards Points: 384
Ground wires have nothing to do with the receptacle not working.
You need to describe the wiring and how youo connected it to the switch.
If the unit will not reset, it is because there is no power to it.
Old 12-03-2012, 03:25 PM   #9
A "Handy Husband"
rjniles's Avatar
Sounds like you do not have a neutral. The white wire to the new GFCI should be connected to the white wire in the back of the box under the red wire nut.
Old 12-03-2012, 04:49 PM   #10
Rochsolid's Avatar
What is that black to white wore joint for?
Rochsolid is offline   Reply With Quote
Old 12-03-2012, 06:31 PM   #11
Thank you all for your help, I ended up calling an electrician out to help! You were right, there was no neutral wire in the box...he ran a new neutral from the bare wire connections already in the box, and I couldn't have figured this out on my own...luckily he was nice enough not to charge me, happy holidays to me!
Old 12-03-2012, 06:36 PM   #12
jbfan's Avatar
Rewards Points: 384
If he connected to the bare wire he is a hack.
You have a worse situation then the had before.
The bare wire is ground and should not carry current.
The Following User Says Thank You to jbfan For This Useful Post:
rjniles (12-03-2012)
Old 12-03-2012, 10:31 PM   #13
kbsparky's Avatar
He is not a good electrician.
He didn't charge you because he is a hack, and you have no recourse against him for a blatant Code violation.
The bare ground wires are NOT designed to be current-carrying for normal circuit operation. You have a potential serious problem on your hands now.
Get a REAL electrician to fix this!
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
jbfan (12-04-2012)
Circuits in Garage and GFCI tedallen Electrical 19 05-24-2012 07:03 PM
Bathroom GFCI Outlet trouble RyG1357 Electrical 3 08-20-2011 03:40 PM
Help with an exterior GFCI Outlet!!??!! Brad2723 Electrical 1 03-31-2010 09:46 PM
What did i do wrong? - Outlet install trips breaker nymex Electrical 22 05-07-2009 02:44 PM
GFCI Outlet jamiedolan Electrical 8 09-28-2008 02:27 PM