GFCI In Middle Of Circuit - Electrical - DIY Chatroom Home Improvement Forum
Old 11-29-2011, 06:43 PM   #1
Rewards Points: 268
GFCI in middle of circuit
So, since I'm not working, I volunteered to help a friend remodel his kitchen. Part of the job is replacing all the outlets and switches, as well as installing 3 can lights. The can lights replaced a strip that held 3 small spot lights, so the electric was existing.
The problem is this, when I install the GFCI, the outlet will not reset. When I push the reset button, in instantly trips. Also the lights don't work. IF I re-install the old outlet, all works well. I changed some other outlets on a different circuit, and they work fine. So, wassup?
packer_rich is offline   Reply With Quote
Old 11-29-2011, 07:49 PM   #2
Rewards Points: 115
are line and loads hooked up properly? what is downstream of gfI?
pokey is offline   Reply With Quote
Old 11-29-2011, 07:50 PM   #3
Electrical Contractor
jbfan's Avatar
Rewards Points: 650
If the gfci is correctly installed, then you have a problem somewhere.
Was the old receptacle a gfci?
Old 11-29-2011, 07:51 PM   #4
Rewards Points: 268
I double checked the lines and loads and I think they are right. the only load are the 3 can lights we installed. Thanks
Old 11-29-2011, 07:56 PM   #5
Rewards Points: 268
The old receptacle was not gfci. I'm just wondering if the can lights themselves could be the problem. All the wiring for the cans is secured with wire nuts and taped. Solid wire throughout.
Old 11-29-2011, 08:00 PM   #6
I'd use this troubleshooting approach:
1. remove the GFCI recept completely from the box, and wire the line and load together, then test. If they work, then you've isolated the issue to something to with the GFCI (either defective or installation problem).
2. connect the GFCI recept to the line, but leave the load unhooked and test. See if the GFCI resets and tests correctly.
If step 1 works, but step 2 fails, and you are positive that the lines are connected correctly to the GFCI, then the device is faulty.
If step 1 fails, then you have a wiring problem on the load side (loose connection shorting in one of the cans, possibly).
If step 1 and step 2 work, I would use pigtails to connect the load to the light cans to the incoming line, and to the line side of the GFCI. Light cans do not need to be protected by a GFCI. If you have other receptacles downstream of the GFCI which must also be protected, this may not be option.
clashley is offline   Reply With Quote
Old 11-29-2011, 08:12 PM   #7
Rewards Points: 268
Thanks for the info. I wiiltry those steps tomorrow. I also googled the GFCI and after a lot of choices, I found a link that showed hooking the load to the line if the load does not need to be protected. Since the lights are the only thing on the load side, I can always do that. But first I'm going to check all my previous connections. Thanks
Old 11-29-2011, 08:16 PM   #8
liscenced electrician
Rewards Points: 538
Either you have the line and load backwards, or the nuetral is touching ground in the can lights
Disconnect the gfci and test the continuity between the nuetral and ground. There shouldn't be any if they are downstream of the gfci and the gfci is removed
jimmy21 is offline   Reply With Quote
Old 11-29-2011, 09:04 PM   #9
jbfan's Avatar
Rewards Points: 650
Not a good idea!
If you truly have a ground fault conition, you are just going to mask the problem for someone to find by accident.
You need to find where the problem is.
Code does not allow light on the kitchen circuits anyway.
The Following User Says Thank You to jbfan For This Useful Post:
mpoulton (11-30-2011)
Old 11-29-2011, 09:18 PM   #10
joed's Avatar
Rewards Points: 13,738
You can't put lights on the GFCI counter circuits in a kitchen. It is a code violation.
Old 11-29-2011, 09:48 PM   #11
I don't think the OP is talking about new construction. If the existing wiring was AHJ-compliant at the time of construction, I don't see the problem with adding a safety device to the existing circuit.
Old 11-30-2011, 06:55 AM   #12
Rewards Points: 268
Thanks for the info. We are just trying to upgrade the counter top outlets to GFCI. We think that this is an improvement and safer than the way it was, with unprotected outlets.
Old 11-30-2011, 07:24 AM   #13
Rewards Points: 1,548
More correctly, hooking the downstream continuation wires to the feed wires and line side terminals leaving the load side terminals of the GFCI empty. Perfectly okay when downstream does not need protection or has additional GFCI units.
Before hooking up the downstream continuation wires, it is a good idea to check for and correct any ground fault downstream as described above.
Old 11-30-2011, 07:35 AM   #14
Rewards Points: 786
disconnect all wires form breaker box (neutral and hot) and check between neutral and ground with a ohm meter, it should be open.
carmusic is offline   Reply With Quote
Old 11-30-2011, 08:07 AM   #15
joed's Avatar
It's not existing. He is installing new can lights.
Adding GFCI but leaving existing circuit Strugglin Electrical 1 10-26-2011 12:15 PM
GFCI Circuit as2637 Electrical 9 03-27-2009 03:41 PM
20A GFCI on 15A circuit jheavner Electrical 35 10-16-2008 03:45 PM
Can a GFCI protected light be installed into a normal light circuit? boongywoongy Electrical 6 05-19-2008 08:02 PM