All of this has to do with a pool
I am adding a 30amp subpanel rather than upgrading my current 30 amp panel due to wire cost. ($1 ft) at lowes for #6 THHN if I upgrade to a 50amp.
So i have almost entire spool of #10 black. I have about a 32' run from my main to the sub. So I would only need to purchase around 40' of #10 white.
I am assuming (tell me if I'm wrong) I can just loop my ground from 1 sub panel to another or if I have to run all the way back to the main.
My current sub has 2 20amp SP GFCI breakers feeding back to the 30 amp DP breaker at the main.
On this new panel, I want to GFCI protect it at the main and use standard breakers on the sub.
Reading Section 680 only suggests I need GFCI protection for my equipment and doesn't specify if it should be on the branch circuit or at the feeder except for the light niche, which is on the original sub panel being protected by a 20amp gfci breaker.
So now if I haven't completely confused you :-), my question stands - can I run my new cables in the same conduit? It would be THHN cable BTW - all code. It is 3/4" electrical PVC conduit. (All passed code 4 years ago).
Also, tell me if you see kinks in my current plan.
The one thing I know I will hear is, that GFCI in the main can be a !@#$ if it starts tripping, b/c I won't know which branch circuit is causing it. I understand that, but my funds are limited, and this doesn't sacrifice safety just would make my troubleshooting more of a PITA.