Old 10-15-2012, 10:49 PM   #1
gfci breaker tripping
hi.i have double pole 15 A gfci breaker and i wired 2 split oulets using 14x3 wire. as soon as plug anything the breaker trip.
fredy is offline   Reply With Quote
Old 10-16-2012, 12:12 AM   #2
Semi-Pro Electro-Geek
I'd bet money that you wired the neutral from the receptacles to the neutral bar in the panel. It needs to go to the neutral terminal on the breaker, and the white wire from the breaker goes to the neutral bar in the panel.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Old 10-16-2012, 07:48 AM   #3
JOATMON
ddawg16's Avatar
yep....
Hey poulton....I thought that on the double GFIC, you couldn't do spit outlets like that since the load on one side would not be the same as the other? In other words...the double GFIC is for 240Vac applications only.
Enquiring minds want to know..........
Common Sense is like Deodorant. Those that need it the most don't use it.
My
and
ddawg16 is online now   Reply With Quote
Old 10-16-2012, 08:00 AM   #4
Originally Posted by ddawg16 View Post
yep....
Will agree with this. MWBC will not work with double pole GFCI breakers.
The imbalanced load will trip every time, as ddawg described.
Gac66610 is offline   Reply With Quote
Old 10-16-2012, 12:52 PM   #5
No, you definitely can do a MWBC with a double pole GFCI. Think about a 120/240V hot tub installation - they all have both 120V and 240V loads. Also, otherwise the neutral terminal on the breaker would be useless. Double pole GFCI's run all three conductors (both hots and neutral) through the current sensor. That way, the breaker analyzes the net current on all three wires, not just the two hots, to determine if there is "missing" current greater than 5mA. This circuit will definitely work if wired correctly.
The other possible reason for the tripping could be an inadvertent connection between neutral and ground somewhere on the circuit.
The Following 2 Users Say Thank You to mpoulton For This Useful Post:
ddawg16 (10-16-2012), stickboy1375 (10-16-2012)
Old 10-16-2012, 01:31 PM   #6
I don't (or haven't seen) a hot tub with 120v, in general they are 240v with a transformer to run low voltage, as in controls and lights.
MWBC will not work on GFCI double pole breaker.
I will agree that we disagree.
Old 10-16-2012, 05:01 PM   #7
Master Electrician
That's funny because a two poke gfci breaker split is actually a code option up here for kitchens. I'll bet you a million dollars it will work. The breakers designed for mwbc operation.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
The Following User Says Thank You to andrew79 For This Useful Post:
Old 10-16-2012, 05:26 PM   #8
E2 Electrician
stickboy1375's Avatar
It will work, you just don't understand how they work.
stickboy1375 is online now   Reply With Quote
Old 10-16-2012, 05:28 PM   #9
E2 Electrician
What imbalanced load? a double pole GFCI breaker will monitor the two hots and the neutral...
Old 10-16-2012, 06:26 PM   #10
Then you haven't seen many hot tubs, and you have very little experience with double pole GFCI's. This isn't a matter of personal opinion to disagree about - it's fact. I've use several 2-pole GFCI's for 120/240V loads, and I have seen many more 2- and 3-pole GFCI's used for loads that include a neutral. It's hard to believe that you would think this if you've ever even handled one of the breakers. They have a neutral terminal right there on the breaker. That would be entirely useless if it couldn't operate with line-to-neutral loads. If you need more evidence, Siemens' product literature describes 2-pole GFCI breakers as "120/240V":
https://images.tradeservice.com/gjPi...AE02263_15.pdf
Old 10-16-2012, 06:30 PM   #11
E2 Electrician
The GFCI electronics require a neutral connection to function, so even with 240v loads, the GFCI breaker requires a neutral connection. Just pointing this fact out.
Old 10-16-2012, 06:52 PM   #12
Let me see if I understand this correctly.
A 2 pole GFCI breaker will work on a split receptacle with a shared neutral, as in the OP?
Sorry I caused a stir, but everything I theorized with GFCI this should not work.
I stand corrected.
And you are correct, I don't do many hot tubs (happily)
The Following User Says Thank You to Gac66610 For This Useful Post:
Old 10-16-2012, 06:55 PM   #13
E2 Electrician
I stand corrected.
Not sure how you are looking at the scenerio, but the breaker will monitor both hots and neutral... This is why they make 2 pole afci breakers as well.
Old 10-16-2012, 06:58 PM   #14
E2 Electrician
Why wouldn't it work? the GFCI protection is at the beginning of the circuit, so the current out, equals the current in... regardless.
The Following 2 Users Say Thank You to stickboy1375 For This Useful Post:
andrew79 (10-19-2012), mpoulton (10-16-2012)
Old 10-16-2012, 09:47 PM   #15
JOATMON
ddawg16's Avatar
mpoulton is right....and sticky, good diagram.....
It had not occured to me that they would run more than 2 wires through the coil.....but....in reality...you could run a 100 wires through it....as long as the currents going one direction are equal to the currents coming back....no current induced in the toroid....
Which explains why it is so important for the neutral for that ckt to be connected to the neutral lug of the breaker.
My
and
AFCI Breaker Keeps Tripping Muinchja Electrical 30 08-25-2011 05:54 PM
UPS tripping 20A GFCI in basement bensec01 Electrical 15 09-18-2010 01:58 PM
20 amp GFCI breaker pops when pool pump is turned on. jagrunner Electrical 11 03-19-2010 05:31 PM
Random GFCI tripping, Data Rack theatretch85 Electrical 5 07-10-2009 09:20 PM