Old 07-24-2012, 02:21 PM   #1
gfci breaker
carmst is offline   Reply With Quote
Old 07-24-2012, 05:02 PM   #2
"So I Re-Wired It"
MisterZ's Avatar
gfci breaker
Are the wires hooked to the correct screws?
It makes a difference which set of screws you use.
One pair is for the gfi outlet, and the other pair to supply gfi protection to another device.
Wired upside down will result in non-gfi protected outlet.
MisterZ is offline   Reply With Quote
Old 07-24-2012, 05:16 PM   #3
gfci breaker
Originally Posted by carmst
gfci breaker does not trip when tested
, the panel breaker does
why?
Is the white pigtail wire of the gfci connected to the neutral buss bar or wire nutted with the load white wire. It won't test if the pigtail doesn't go to the buss bar.
curiousB is offline   Reply With Quote
Old 07-24-2012, 11:06 PM   #4
gfci breaker
Yes curious they are connected correct. I have 4 gfci's and none of them are triping. they eeach have their own 20 amp breaker in the panel ande all of the breakers willl trip but nopt any of the gfci's. I bought them from wal mart. could they possibly all be defective?
Old 07-24-2012, 11:08 PM   #5
gfci breaker
Msiter z they are in the correct place. and as i told curious, none of the 4 gfci's will trip
This is all new wireing and a new panel box.
any ideas?
Old 07-24-2012, 11:11 PM   #6
"So I Re-Wired It"
MisterZ's Avatar
gfci breaker
It is quite possible they are defective. Four in a row may be stretching it, but its possible.
Just curious, how are you testing these?
Old 07-24-2012, 11:27 PM   #7
gfci breaker
Old 07-25-2012, 05:58 AM   #8
Master Electrician
gfci breaker
Originally Posted by carmst View Post
I am using a #14 wire stripped 1/2 inch on both ends and holding it with rubber coated side cutters. This is correct am I right? Like a kid sticking a bobby pin in it except with rubber to protect me
OMG! That's brilliant!
brric is offline   Reply With Quote
The Following User Says Thank You to brric For This Useful Post:
jbfan (07-25-2012)
Old 07-25-2012, 06:03 AM   #9
Electrical Contractor
kbsparky's Avatar
gfci breaker
Let me get the straight: You're "testing" your GFCI receptacles with a dead short between the slots of the outlets?
That will certainly blow the circuit breaker. And quite possibly damage the GFCI circuitry in each device.
What happens when you press the "test" button on those outlets?
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
MisterZ (07-25-2012)
Old 07-25-2012, 07:46 AM   #10
Master Electrician
gfci breaker
While your at it why dont you try it with a capacitor instead of a wire. If your going to try and hurt yourself might as well do it right.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 07-25-2012, 07:52 AM   #11
gfci breaker
The OCPD is doing exactly what it should be doing in this case. Protecting the circuit from a dead short. GFCI's do not trip in the event of a dead short, thet trip when current leakage is detected. The circuitry in a GFCI monitors the incoming and outgoing current flow to see if it is the same. When the current flow back thru the neutral is lower than the hot then the device senses it and trips. In a dead short, the current flow on the neutral is the same as the hot so the GFCI will not see the event.
danpik is offline   Reply With Quote
The Following 2 Users Say Thank You to danpik For This Useful Post:
DangerMouse (07-25-2012), jeffnc (07-25-2012)
Old 07-25-2012, 08:19 AM   #12
Master Electrician
gfci breaker
Anyone want to nominate this person for a Darwin award?
Licensed Master Electrician
Commonwealth of Virginia
busman is offline   Reply With Quote
The Following User Says Thank You to busman For This Useful Post:
gregzoll (07-25-2012)
Old 07-25-2012, 09:25 AM   #13
gfci breaker
Finally, someone who understands how GFCI works. I've talked to licensed electricians who do not understand this.
This is why GFCIs do NOT protect you from electrocuting yourself if you touch the hot and neutral on the same device. No current is leaking to a "ground" outside of the circuit.
What the OP described is working exactly like it is supposed to. Assuming he is shorting the hot to the neutral, then the panel breaker should trip and the GFCI should not. This is actually a valid test I suppose, to make sure your GFCI is working correctly.
A lot of people also think a GFCI needs to be connected to ground to work correctly. Maybe GFCI is a bit of a misnomer because it confuses a lot of people. Instead of GFCI maybe it should be CLCI - Current Leak Circuit Interruptor. Or EGFCI - External Ground Fault Circuit Interrupter.
jeffnc is offline   Reply With Quote
Old 07-25-2012, 09:30 AM   #14
gfci breaker
Seconded!
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 07-25-2012, 10:33 AM   #15
gfci breaker
How do you arrive at this? You haven't said anything to convince me of it.
A GFCI breaker should trip when the test button is pressed if only it is plugged into the panel and the neutral pigtail is terminated on the neutral bus. Nothing needs to be connected on the load side. I would sort out that most simplest scenario before even connecting a load.
Honestly, you don't seem to be very knowledgeable in such matters and since GFCIs are for protection this might be one time to call up a professional. Do you really want protection devices that don't protect? Who in your family can you live without?
The Following User Says Thank You to curiousB For This Useful Post:
andrew79 (07-25-2012)
Dimming lights on one circuit, GFCI breaker tripped boatman537 Electrical 4 06-05-2012 11:43 AM
GFCI Breaker Gzuber Electrical 7 05-30-2012 11:38 PM
Switch triggering GFCI breaker on a DIFFERENT circuit stillmarried Electrical 5 11-29-2009 10:14 PM
GFCI Breaker & GFCI Outlet together??? abinpa General Discussion 6 04-12-2009 09:59 PM
GFCI Recepticle vs. Breaker WaldenL Electrical 19 01-18-2009 01:04 PM