I am in a 35 year old home with AL wiring. I have several outdoor and shaver r ceptacles I wish to upgrade to GFCI. Is there one out there rated for aluminium wiring or can I pigtail copper and paste with alu rated connectors ?
Every GFCI I have seen says not for aluminium wiring
Chemist1961 is offline   Reply With Quote
Old 04-05-2009, 11:48 AM   #2
Circuit
Find out which circuit it is and install a ground fault circuit breaker , your covered all the way.
SULTINI is offline   Reply With Quote
Old 04-05-2009, 11:59 AM   #3
Good plan thanks, but my other concern is weather exposure on the contacts outside so I thought an outside GFCI receptacle would work best.
So is there an AL rated GFC breaker that fits an FPE Stab Lok panel
Old 04-05-2009, 12:34 PM   #4
you may want to seriously think about changing that FPE panel!!...the breakers are infamous for NOT working!...also, i prefer to usea gfi at the point of use as opposed to gfi breakers...
NolaTigaBait is offline   Reply With Quote
Old 04-05-2009, 12:39 PM   #5
FPE and AL, AL is ok if done right, fpe is not ok.
In the most recent independent tests of FPE Stab-Lok equipment, using a larger pool of FPE Stab-Lok circuit breakers than the older CPSC and Wright Malta tests found significantly higher failure rates of FPE Stab-Lok circuit breakers, including a look at critical safety failures (breaker failed to trip at 200% of rated current or jammed) which found up to 80% failure rate for FPE Stab-Lok GFCI circuit breakers (n=4), 12% failure rate for double pole FPE Stab-Lok circuit breakers (n=120), and a 1% failure rate for FPE Stab-Lok single pole circuit breakers (n=345).
http://www.inspect-ny.com/fpe/fpe.htm
rgsgww is offline   Reply With Quote
Old 04-05-2009, 02:50 PM   #6
!) Use copper pigtails on the GFCI.
2) Find GFCI receps with pigtails instead of terminals (if they still make them)
220/221 is offline   Reply With Quote
Old 04-05-2009, 03:46 PM   #7
Electrician
Rewards Points: 800
Please note that this poster lives in Ontario where FPE=Federal Pioneer not Federal Pacific.
It is a trade joke(with some truth) that federals do not trip. The newer breakers apparnetly don't have this issuse.
darren is offline   Reply With Quote
Old 04-06-2009, 05:59 AM   #8
Thanks for making that point Darren.
Yes I forgot to post that info. I had heard feed back about Fed Pac before. Thanks to all of you for the concern.
I would like to rewire the entire house over the next while since some insurance companies are now opting out of coverage. I have been here 19 years and had one incident of a new microwave overheating at a receptacle. I ran a fresh circuit as required by code and had the entire system inspected by a senior inspector who's been around ALR for quite awhile.
In addition, as a precaution I have replaced every connector with ALR rated ones and paste and inspected and applied paste and or pigtailes throughout the house at lighting , etc. But I'm still concerned about future insurability
Old 04-06-2009, 07:49 AM   #9
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
I thought in Canada the only acceptable method for copper to aluminum was the copalum crimp?
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 04-06-2009, 04:04 PM   #10
CO/AL crimp?
Stubbie,
Not according to my inpsector who works the Provincial Hydro Authority, We have CSA approved and I believe UL approved CO/AL connectors from MARR and IDEAL makes a gel filled one as well. Both are sold in this area.
Never seen this crimp device or heard of it. Looks like a product from AMP if I am reading the heat shrink. I have their crimpers. Good tools and terminals in my experience. Thanks.
Old 04-06-2009, 05:10 PM   #11
Rewards Points: 35
Wink
GFCI Receptacles for Aluminum Wire
I performed a search awhile back for GFCI receptacles that were rated for use with aluminum wire and I found that none of the common manufacturers make an Aluminum compatible receptacle. The only solution I found was to use copper pigtails.
Use of the Copalum devices requires that you locate a trained contractor that is certified to install the devices with the leased AMP equipment. Another good solution for connecting copper pigtails to aluminum wire is to use Alumicon aluminum to copper lugs. The lugs are small, insulated, terminal bars that are rated for both aluminum and copper wires, so there is no issue about twisting aluminum and copper wires together as when you use an Ideal 65 twist connector. The alumincon connectors are expensive ($5+ each) but they work great with no downside other than the cost.
czars is offline   Reply With Quote
Old 04-06-2009, 07:31 PM   #12
An aluminum crimp doesn't seem like a good idea. The stuff is too fragile/soft.
Tags
al wiring , aluminium , gfci
GFCI with no ground wire? gante Electrical 6 03-13-2009 09:17 AM
Gfci Circuit howard.wheaton Electrical 10 01-29-2009 05:14 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM
GFCI Question Mdbuilder Electrical 6 06-19-2008 03:15 PM
Best way to wire this Bathroom? GFCI, Drawing inside twilightcall Electrical 31 01-21-2008 09:29 AM