GFCI after dimmer switch
Just had a situation that was strange. Chandelier style light fixture above soaker tub. Protected by GFCI in adjacent walk in closet (GFCI dedicated to light fixture only). Line side of GFCI ran back to a wall switch then to branch circuit power source. The switch was a slide dimmer.
The odd thing is that when dimmer was on 100% the gfci would trip and reset fine. Set the dimmer less than 50% and it would trip fine with test but wouldn't reset. Set dimmer close to zero and it would neither trip or reset.
The fix was a pain. The gfci needed to be ahead of the dimmer switch. In other words the dimmer needed to be on load side of gfci with the fixture. The way the wires ran the power source was with the dimmer but not enough conductors to the closet gfci location.
So in the end had to cut out a three gang wall box and put in a 4 gang box and put a dead front gfci beside the dimmer switch. I then eliminated the down stream gfci and put a blank cover over that box.
I just wonder if the original electrician knew he was faking a gfci install after the dimmer and was just too lazy to make it right...
What about a chandelier style fixture above the tub. Does that have to be a wet rated fixture. It is quite high so you can't touch it standing in tub (maybe Shaquille could)..
Is it a code violation to put a dimmer (or any switch) ahead of a gfci? Or just poor common sense?
curiousB is offline   Reply With Quote
Old 04-07-2013, 10:46 AM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
(D) Bathtub and Shower Areas. No parts of cord-connected
luminaires, chain-, cable-, or cord-suspended luminaires, lighting
track, pendants, or ceiling-suspended (paddle) fans shall
be located within a zone measured 900 mm (3 ft) horizontally
and 2.5 m (8 ft) vertically from the top of the bathtub rim or
shower stall threshold. This zone is all encompassing and includes
the space directly over the tub or shower stall. Luminaires
located within the actual outside dimension of the bathtub
or shower to a height of 2.5 m (8 ft) vertically from the top
of the bathtub rim or shower threshold shall be marked for
damp locations, or marked for wet locations where subject to
shower spray.
Old 04-07-2013, 10:50 AM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,864
I would think it was common sense to not dim a GFI. You say an electrician did the original install?
Old 04-07-2013, 11:03 AM   #4
Rewards Points: 776
Yes home builders electrician did it this way. As built. House is only 8 years old.
Based on code reference even with gfci this is an illegal use of fixture? I went and measured, lowest point of fixture is 80" from bottom of tub, 63" from water level at overflow height.. Yikes.
Does code state no switch permitted on line side of gfci's?
Old 04-07-2013, 11:19 AM   #5
k_buz's Avatar
It is completely legal to switch a GFI. However, you cannot dim a receptacle. The fixture install is violating the clearances and should never had been passed. I would also question the damp location rating.
The Following 2 Users Say Thank You to k_buz For This Useful Post:
Jim Port (04-07-2013), stickboy1375 (04-07-2013)
Old 04-07-2013, 11:36 AM   #6
Rewards Points: 776
Maybe a nit but permitting switching of line side of gfci renders test reset inoperable which could be confusing if switch and gfi are not near each other. Further if a dimmer is installed then it won't work properly except at 100%. That may compromise gfci operation at dimmed levels.
Old 04-07-2013, 11:43 AM   #7
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Just for examples, this picture below is 100% code compliant.... No GFCI required.
The Following 2 Users Say Thank You to stickboy1375 For This Useful Post:
busman (04-07-2013), Speedy Petey (04-07-2013)
Old 04-07-2013, 11:58 AM   #8
Rewards Points: 776
How is lower pict compliant? That seems inside keep out zone. What am I missing?
Old 04-07-2013, 11:58 AM   #9
E2 Electrician
Look at the TYPE of fixtures required to be out of the zone...
Old 04-07-2013, 01:48 PM   #10
Semi-Pro Electro-Geek
Rewards Points: 2,892
Even if it were a deadfront GFCI, you couldn't dim it - it violates the voltage ratings of the device, since it is listed to be used only at 120V. It will, in fact, not properly provide GFCI protection except when the dimmer is close to fully on.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Old 04-07-2013, 01:50 PM   #11
I'm not so sure those sconces look damp-rated.
Old 04-07-2013, 01:57 PM   #12
E2 Electrician
I installed them, they are UL listed with a damp rated location sticker on them.
Old 04-07-2013, 02:03 PM   #13
Rewards Points: 776
I know that is why I put in dead front gfci ahead of dimmer. Are you saying dimming on load side of gfci is not allowed?
Old 04-07-2013, 08:48 PM   #14
NO. Dimming on the LINE side is not allowed.
Old 04-07-2013, 09:45 PM   #15
Wow. Are the lamps enclosed inside the fixture?
replacing an existing 1-way decora light switch with a dimmer switch maljeff Electrical 3 01-11-2012 12:49 PM
Help Wiring Dimmer Switch scubakathy84 Electrical 2 12-21-2011 11:26 PM
3 Way Dimmer Light Switch Problem psubaron Electrical 4 07-13-2011 09:08 PM
fan/light switch buzzing mjlocat Electrical 4 05-23-2010 03:44 PM
Weird problem replacing dimmer switch cdale600 Electrical 9 01-20-2009 09:31 AM