Getting New Home Runs Into Attic - Electrical - DIY Chatroom Home Improvement Forum
Old 08-10-2012, 11:17 PM   #1
Thadius856's Avatar
Rewards Points: 504
Just pulled 7 home runs for kitchen remod. All come across the attic and come out in a 1.5" hole in a rafter blocking. I have about 15' hanging on each 12-2.
The problem is I have farther than 24" to get into the panel, so i dont get the nipple exception to my conduit. Since they're required to be 20A (except the lughing circuit?) i dont have any room for derating.
Is my only choice to run three separate EMT 3/4" and drill new holes in the side of my panel?
Edit: would a junction help me at all?
Check out my on-going Project Thread!
Current Project: Whole House Data Wiring
Back Burner: Drywall Patching
Planning: Kitchen Reno
Thadius856 is offline   Reply With Quote
Old 08-10-2012, 11:40 PM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
If you are using romex, you can use a romex connector and forgo the conduit.
Old 08-10-2012, 11:57 PM   #3
Thadius856's Avatar
Rewards Points: 504
To be clear, this is the main panel on the outside of an exterior wall and I'm trying to get them up fom the panel and into the attic through the rafter blocking.
Old 08-11-2012, 12:37 AM   #4
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
This is what I would do, either open up the sheathing behind the main panel to get the new circuits into the panel with separate NM connectors, OR do a pipeline from the main panel to the attic, with approved jboxes and thhn...
Old 08-11-2012, 01:17 AM   #5
Thadius856's Avatar
Rewards Points: 504
I'll try to get into the wall in the morning. Going to be tough. Will see what I can do.
Old 08-11-2012, 05:39 AM   #6
Rewards Points: 1,192
F'ed up eh? Don't hide mistakes where down the road nobody can find them.
bobelectric is offline   Reply With Quote
Old 08-11-2012, 10:11 AM   #7
Thadius856's Avatar
Rewards Points: 504
Not trying to hide anything. If pulling them into the stud bay behind the main panel and bringing tem through the back isn't the right way to do it, please let me know. I definitely want to Do It Right. That's why I'm asking here and not just hacking things in willy nilly.
Is the 3x 3/4 emt route better?
Is 1x 2" sch 40 PVC with jb 20" up better?
Is there a better way I haven't considered?
Old 08-11-2012, 10:20 AM   #8
Thadius856's Avatar
Rewards Points: 504
If I went the THHN route, #12 is would be derated to 70% (7-9) for 21A.
Neutrals don't count as current carrying conductors in this case.
I'd need to pull white and green, and one other color that should probably be black or red but doesn't have to be if I remark it.
Is this all correct?
To keep the cursing to a minimum, what size conduit would you recommend I pull these through?
Old 08-11-2012, 10:26 AM   #9
E2 Electrician
You wont have any derating issues until you cross over 9 conductors.
Only if they are multi wire branch circuits.
I'd need to pull white and green, and one other color that should probably be black or red bu doesn't have to be if I remark it.
You need to pull a neutral for every two ungrounded (hot) conductors...
In your example, you have 7 circuits, im just assuming they are all two wire circuits, you would need to run 7 hot conductors and 4 neutral conductors and 1 ground sized to the largest branch circuit you already ran to the kitchen. Only ONE of the neutrals would be considered current carrying. Giving you a total of 8 current carry conductors.
3/4 EMT with 12 #12AWG conductors is only a fill % of 28.96%, so the jam probability is very small... Personally I would pull one spare wire to complete the last multi wire branch circuit, meaning, I would pull 8 hots, 4 neutrals, and 1 ground... you must pair up these wires as to ensure you don't over load any of the neutrals, they must be landed on opposite phases for the neutral current to be cancelled out.
Old 08-11-2012, 11:10 AM   #10
Thadius856's Avatar
Rewards Points: 504
Awesome! The only nasty part will be making all these connections in an unfinished attic.
I'm with you until the very last part. I want each of the 4 neuts to share one leg from each phase. How can I determine which breaker is on which leg? Silly question, I know...
Old 08-11-2012, 11:15 AM   #11
k_buz's Avatar
I wouldn't switch over to THHN. I would install as many sleeves as necessary (4 3/4 PVC). You are just asking for trouble with all those splices.
Old 08-11-2012, 11:17 AM   #12
E2 Electrician
Just use two pole breakers and you will be fine. and label your hots so when you are in the attic, you know how to pair them off. (example... label the conductors, 2,4 6,8 10,12 14,16.... this way you know 2 & 4 share a neutral which would also be labeled 2,4... This will ensure that you keep everything in check.
Old 08-11-2012, 11:23 AM   #13
E2 Electrician
You cant do that, code wise... And I think the OP will be fine as long as he takes his time and labels all the thhn's....
Old 08-11-2012, 12:23 PM   #14
k_buz's Avatar
For my information...why? We don't do alot of meter/main's round here so I'm not up on the ins and outs of it. Its not underground so its not considered a wet location.
Old 08-11-2012, 12:29 PM   #15
E2 Electrician
Check out 312.5 (C) Cables. It can be legal, but rarely is... you have to meet 7 criteria's
This applies to Cabinets, Cutout boxes, and meter socket Enclosures... Not just meter main cabinets... I see a lot of panels with all the NM's just stuffed into a 2" PVC conduit....
The Following User Says Thank You to stickboy1375 For This Useful Post:
Thadius856 (08-11-2012)
Insulate Attic, solar screens, attic fan- biggest bang for buck? heidabear Insulation 6 08-04-2012 12:25 AM
Attic project - Would like opinions whataboutj Insulation 6 06-29-2011 04:07 PM
Attic venting questions lemmy Roofing/Siding 36 05-28-2011 09:14 PM
Ventilating attic with two roofs senorbungle Building & Construction 2 01-09-2011 05:17 PM
Attic fan options P550 Roofing/Siding 1 08-22-2010 01:47 PM