Old 11-12-2011, 02:17 AM   #16
" Euro " electrician
frenchelectrican's Avatar
generator transfer switch neutral
Originally Posted by KE2KB View Post
Are all portable generators now being supplied with GFCI breakers, or just those that are certified for use in construction sites?
FW
Per current codé they supposed to be on it but some generators do not have GFCI on it { that is getting less and less due the codé change }
Merci,
Marc
Old 11-15-2011, 11:05 PM   #17
Merci,
Marc
So, the neutral should NOT be bonded to the ground on the generator, or else there will be multiple return paths, causing the GFCI to trip.
Frame of gen gets bonded to SE ground electrode (outside the house), and I can use a standard transfer switch; don't need neutral switching.
Is this correct?
FW
KE2KB is offline   Reply With Quote
Old 11-16-2011, 07:24 AM   #18
Ideally yes.
Problem is, for some generators you can't unbond neutral and ground within without tearing the generator apart which I don't want to do.
The average homeowner who lost his house in the Oklahoma tornadoes should move for good and not rebuild. Too much complexity watchdogging the contractor. Too much a chance to be defrauded.