generator transfer switch neutral
The information I have seen on the web on how to hook up transfer switches has seemed pretty unclear.
It would seem simplest to disconnect (float) the generator neutral from the ground - ground the generator chassis - and connect the generator neutral through the transfer switch to the breaker box neutral. I assume the breaker box neutral is always connected to the ground? If the generator ground and neutral are left bonded, I assume you would need to somehow wire the breaker box so that the breaker box ground can be disconnected from the breaker box neutral? |
I am not say8ing you should do it this way but:
Sometimes the main panel neutrals and grounds need to be separated, say, for compatibility with an upstream (whole house) transfer switch or an upstream main disconnect switch. But I would not separate the neutrals and grounds of what has been my main panel for the sole purpose of accommodating a particular generator. It would be better to separate ground and neutral at the generator. But if this cannot be done easily then I would be tempted to not connect the green wire running between the generator and the rest of the system,and set the generator on a wood or other insulating platform. This prevents the "neutral" current from splitting itself between the white and green lines back to the generator and tripping a ground fault interrupter built into the generator. Or if the generator did not have built in GFCI's that kept tripping, leave neutral-ground bonding in place in both the main panel and the generator. |
Thanks. |
There is no reason to tamper with the generator at all. It is not a separately derived system.
All part of the grounding electrode system. |
OSHA requires generators used at construction sites and so forth to have GFCI protection...
However these GFCI's trip when connected to a regular transfer switch! (Considered a "non-separately derived system" because the neutral from the generator is connected to the service panel neutral.) But you can use a different type of transfer switch called a "neutral switching transfer switch", then this solves the GFCI tripping problem. (Then considered a "separately derived system" as the neutral from the generator is switched and then isolated from the service panel neutral.) |
"Why does the neutral bonding in the generator determine the type of generator panel used? For an answer we refer to the CEC. Rule 10- 400 requires that equipment (generator frames) be bonded to ground. Rule 10-106 requires AC systems to be grounded. Rule 10-204 requires the ground to be located at the service entrance switch or panel. And finally, Rule 10- 204(1)(d) does not allow a connection between the neutral conductor and the grounding elec- trode on the load side of the service entrance panel, effectively this does not allow bonding of the neutral to the ground electrode in more than one location." |
Some of the electricity flows back to the generator via the neutral. And some electricity via the bonding connection in the main electrical panel, then through the ground wire from that panel to the generator ground, then through the bonded ground to neutral at the generator. Thus causing the GFCI to trip. So another solution is to remove the neutral/ground bond at the generator, however the generator is no longer useable for construction sites, etc. and I believe it must be labeled so. For example... http://www.gen-tran.com/assets/pdfs/...Bulletin20.pdf |
I'm still wondering why there's a code against connecting the neutral to the ground in more than one place. Is there some danger, or is it because it could throw off gfci?
One it will trip the GFCI no question asked { this is true with Honda generators but other brands may do the simauir sistuation as well so check that manufacter instruction on the details } Second thing that the main house system the netual and earth { ground } is allready bonded at the main breaker box but once it go out after that it will be seperated the main reason so it can able get the OCPD tripped if any fault show up. Hope this will help ya and I know other guys if they have more info they can chime in as well. Merci, Marc |
Are all portable generators now being supplied with GFCI breakers, or just those that are certified for use in construction sites?
FW |
| All times are GMT -4. The time now is 09:16 PM. |