dhiggins26 01-25-2012 08:21 PM
i am hooking a 7000wt. portable generator to a 10 circuit transfer switch next to my main panel. my question is how much distance can i have between trans. switch and power inlet box before i start to lose noticeable currant ? i plan on using #10wire. depending on the location i choose the distance could be from 30' to 120' with a 10' cord between gen. and inlet box. Would a heavier gauge wire [ # 8 ] make any difference ?
Missouri Bound 01-25-2012 11:29 PM
You have your answer...at 30' you can use the #10...at 120' you can use the #8. Or you can use the #8 for any distance, but at 120' you would suffer some voltage drop. Nothing too severe for temporary usage.
AllanJ 01-26-2012 07:18 AM
This is what I suggest.
Use the 8 gauge wire/cable if the distance from the generator to the furthest eligible receptacle in the house (not the distance from the generator to the transfer switch) is the 120 feet.
Ignore the fact that 12 or 14 gauge wire goes from the panel to the receptacles.
This is an unscientifically derived suggestion. The voltage drop in the generator line depends on the wire size and the amperes delivered at that moment by the generator. The voltage drop in a branch circuit depends on its wires size and the number of amps drawn at that moment in that branch circuit.
biggles 01-26-2012 08:23 AM
i did a #6/4wire on a 100' run between them from a 3500W might even consider #4,but definitly not #10
dhiggins26 01-26-2012 06:17 PM
thank you, much appreciated, DH
dhiggins26 01-26-2012 06:37 PM
MB are you saying even with #8 wire there will still be a voltage drop? I just want to be clear on this. thank you, DH
Missouri Bound 01-26-2012 09:07 PM
I re-read what I typed and I see how it came out a bit confusing. The voltage drop will be minimal with #8, while at that distance you should NOT use #10. 8 is acceptable, and with #8 you will have 1/2 the voltage drop. Sorry for my unclear statement.:eek:
dhiggins26 01-27-2012 09:57 AM
thank you for your response MB,Greatly appreciated!
rrolleston 01-27-2012 11:03 AM
I would use 6 it will not be too much more.
dhiggins26 01-27-2012 11:31 AM
wire gauge
thanks rrolleston, I appreciate your response.
rrolleston 01-27-2012 12:20 PM
Keep in mind you may need to use 6 gauge copper ring terminals with a #10 ring to get all conductors in. I usually solder mine on. Dip wire in flux put connector on crimp it tight heat with torch and add solder.
rrolleston 01-27-2012 04:43 PM
I almost forgot about this until I looked at another thread. Install a ground where you plan to use the generator. Some 10 gauge stranded and a pipe ground clamp connected to bare metal on your generator frame and an acorn clamp on the rod could probably do this for under 20 bucks.
dhiggins26 01-27-2012 06:39 PM
thanks again rrolleston,
dave higgins