Generator Question - Electrical - DIY Chatroom Home Improvement Forum
Old 06-24-2008, 07:22 AM   #1
Generator question
I am helping (trying) a friend that has a 80KW Kohler generator. It is a 3 phase. It has been reconnected to provide single phase. It is a 12 lead and is connected as such
Connected
3,5,9 & 11
1&7 L1
2&8 L2
4,6,10 & 12 Neutral
When started it puts out 277V. This configuration is per the manual.Can you use ant two legs?
Also if it is 3 phase does this wiring change the phases to be 180 degrees or still 120. Does a transformer need to be used. It is to be used to power 10 condos with A/C.
BillyD is offline   Reply With Quote
Old 06-24-2008, 07:43 AM   #2
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
I can't read it too well Billy, but it looks like the only 1ph drawing is the one on the lower left.
wirenut1110 is offline   Reply With Quote
Old 06-24-2008, 08:41 AM   #3
Sorry hope this is better.
Old 06-24-2008, 10:06 AM   #4
Idiot Emeritus
Rewards Points: 1,492
This is called a zig-zag connection. It's a very common way to get 100% single phase output from a 3 phase generator.
This generator was almost certainly connected for 277/480 earlier, and you'll need to find the voltage control and adjust it down a bit.
Rob
micromind is offline   Reply With Quote
Old 06-24-2008, 12:17 PM   #5
Does this mean it is 180 deg. or still 120 degrees and can we use any two legs of the 3 phase circuit breaker?
Thanks for the help
Old 06-24-2008, 12:50 PM   #6
" Euro " electrician
frenchelectrican's Avatar
That connection what i called double zigzag connection and yes it is rated for full 100 % rating if the nameplate stated on that.
For the voltage regulator you will end up have to move the jumper lead to correct voltage reading.
Yes you can use the generator's 3ph breaker [ some will have two breakers so watch out with that ]
After you change the connection you will need to verify the RPM or HZ first then adjust the voltage as need to.
If you try to adjust the voltage first before you adjust the engine speed or verify if running in correct RPM it will be pain in the butt get it right.
once you get it right take your voltmeter to double check aginst the generator voltage gauge to make sure it is correct.
Merci,Marc
Old 06-24-2008, 01:14 PM   #7