I have a Troy Bilt 6000 watt generator that will only be used for power outages. I have been reading about these neutral to ground bonds at the generator and I'm concerned whether I should remove the bond. I installed a reliance transfer switch and thought I was good but now I'm not so sure. Is it imperative to remove this bond or can it be left alone? Will leaving the bond cause any issues with the power supplied to my house from the genset?? Thanks in advance!!
Charlie
Generator neutral to ground bond-image-3881334650.jpg   Generator neutral to ground bond-image-214030999.jpg
Hllywd62 is offline   Reply With Quote
Old 07-27-2013, 08:13 AM   #2
joed's Avatar
Rewards Points: 11,562
Unless your transfer switch switches the neutral you should unbond the neutral and ground in the generator.
Old 07-27-2013, 08:41 AM   #3
If its only for a outage probably unbond it. I don't think it would be safe to power any tools or anything else if its unbonded. I think this is a long subject but a lot of people leave it bonded and don't have any problem unless the gen has gfi reseptacles.
Kpack is offline   Reply With Quote
Old 07-27-2013, 08:52 AM   #4
Rewards Points: 12,824
That box on the side of the house should have been mounted to a siding block.
Done that way there's no way for the siding to expand and contract and will break the caulking seal and may buckle the siding.
Old 07-27-2013, 09:20 AM   #5
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
1) you must read how your generator is wired/bonded ....
2) mainly it would be the function of GFI outlets that would be effected ..
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
Old 07-27-2013, 09:27 AM   #6
Rewards Points: 516
Floating Neutral or Bonded Neutral .... You must check what you have
Here is some info ...
http://members.rennlist.org/warren/honda.pdf
and
http://www.generlink.com/CompatibleGenerator.pdf
Updated: 06/26/2013
all are not wired the same the same .....even within the same manufacture ...
more info:
NOTE: Generators with Full Panel GFCI Protection (Ground Fault Circuit Interrupter) comply with OSHA inspections on job sites. However, these generators will not function when connected to a GenerLink since the home or building main breaker box also has a neutral bonded to ground. When both the generator and the home / building breaker box contains a neutral bonded to ground, the generator's GFCI will open and no outlets will function
* Honda EB Series generator is not compatible with the GenerLink Automatic Transfer Switch. Please contact the nearest Honda dealer for information on modification to the receptacle panel.
NOTE: Per the National Electric Code, all generators must have a "floating neutral " when used with the GenerLink Automatic Transfer Switch. Please refer to the generator operation manual for bonded neutral specifications.
Old 07-27-2013, 09:46 AM   #7
Electrical Enthusiast
Rewards Points: 504
You might also contact the manufacturer with the model number and ask. Mine has a floating neutral, and no GFCI receptacles.
Kyle_in_rure is offline   Reply With Quote
Old 07-27-2013, 09:57 AM   #8
The generator I have doesn't have GFCI outlets, but has breakers for them... Here are pics to help out further...
Generator neutral to ground bond-image-996892859.jpg   Generator neutral to ground bond-image-3967628225.jpg   Generator neutral to ground bond-image-2608026990.jpg
Old 07-27-2013, 10:18 AM   #9
Rewards Points: 504
Well, there's your answer . According to your manual, the neutral is bonded to the ground on this generator.
Old 07-27-2013, 11:00 AM   #10
Yeah, I knew it had a grounded neutral, I was just asking if its imperative that it be removed if attached to a transfer switch that doesn't switch the neutral, or if its ok to leave alone for the occasional times that I will need to use the genset...
Thanks!
The Following User Says Thank You to Hllywd62 For This Useful Post:
Kyle_in_rure (07-27-2013)
Old 07-27-2013, 04:37 PM   #11
joed's Avatar
It will function just fine. but I believe code requires it to be unbonded. The neutral and ground must only be connected at one point in your house.
Old 07-28-2013, 01:43 AM   #12
Electrician
Rewards Points: 150
Turn off the main breaker to the house, hook up the genny and run it.
Bonded or unbonded, GFCI or no, it will do no harm to the house or the genny. If you can cycle all the loads on and off then make no changes. You are good to go.
If the GFCI breaker trips (it will) then you have no choice but to unbond the genny.
Start from the beginning and retest all your loads.
Glennsparky is offline   Reply With Quote
Old 07-28-2013, 09:26 AM   #13
Glennsparky, thanks so much!!... I'll do as you say.... I was just concerned after all I read about these bonded generators... I don't get frequent power outages here on Long Island... But I just didn't want to create a dangerous situation either... Thanks so much!!
Charlie
Philly Master (07-28-2013)
Why not Bond Neutral to Ground on subpanels brianj_92505 Electrical 18 06-27-2013 12:36 AM
running ground for new upgraded 200 Amp service mbaldwin Electrical 11 05-26-2013 10:51 AM
neutral and ground bond on meter box and subpanels in same structure zandroid Electrical 9 05-04-2013 02:20 AM
240 volt load/appliance and ground vs neutral kgize Electrical 7 04-23-2010 12:40 AM
Bonding Ground in Conduit jamiedolan Electrical 5 01-26-2010 11:14 PM