Hello i need to hook up a panel to main box at meter so when my power comes out i can pull out generator and hook generator to box to run power.I seen at someones house but he didnt do it any help please
tity04 is offline   Reply With Quote
Old 11-07-2008, 06:36 PM   #2
DIYer
There's two ways to do this. You can buy a box that has an inlet built in and some switches. It's easy to install and pretty much foolproof.
http://www.hechinger.com/hardware/to...-31406crk.html
This is the one I got. It was only $270 at the local home store though. To use it you put wirenuts in your main panel though and that gives older electricians fits even though the manufacturer says it's OK under the NEC.
The other way is to install a subpanel that has an interlock at the top. This way requires you to do more real wiring, but it's a more expandable way.
http://www.squared.com/us/applicatio...Panels2005.pdf
In addition to that you need a separate inlet with the panel method, since it's not built in. Advantage there is you can install the inlet outside in a weatherproof box which is a little easier than running an extension cord through an open window.
Gigs is offline   Reply With Quote
Old 11-07-2008, 08:13 PM   #3
joed's Avatar
Rewards Points: 12,334
Here's one way that's simple.
http://www.generlink.com/about_generlink.cfm
Old 11-08-2008, 10:37 AM   #4
Rewards Points: 126
There are several approved methods for connecting the generator to your house wiring. The most important thing you must consider is protection for the generator and utility workers (lineman).
Install a twist lock receptacle or plug that fits your generator outside where you will operate it. Run this 4 wire circuit back to a double pole breaker in your main panel or sub panel if you have one. Get a mechanical interlock that prevents turning the main breaker back on if the generator breaker is on, and visa versa. Use this method unless you want automatic operation.
Like this for an example.www.interlockkit.com
Could I move my Meter & Power Drop to the Side of my house? jamiedolan Electrical 9 07-28-2010 05:16 PM
Does it matter how close your panel is to your meter? jamiedolan Electrical 10 10-18-2008 04:38 AM
Clamp Meter Findings jamiedolan Electrical 16 09-08-2008 08:13 PM
Is it normal to change the upper line at the meter when running new supply line? twilightcall Plumbing 3 08-08-2008 11:10 AM
Meter ratings Stubbie Electrical 3 04-02-2008 10:12 PM