Old 08-31-2009, 06:29 PM   #16
Electrical Contractor
 
wirenut1110's Avatar
 
Join Date: Apr 2008
Location: Chester, VA.
Posts: 1,046
Send a message via AIM to wirenut1110
Share |
Default

Generator Install - A few questions...


A picture would be great of your panel and disconnect. I know what the transfer switch looks like. Were you able to find the neutral bar on the transfer switch?

wirenut1110 is offline   Reply With Quote
Old 08-31-2009, 06:41 PM   #17
Newbie
 
Join Date: Aug 2009
Posts: 15
Default

Generator Install - A few questions...


Quote:
Originally Posted by wirenut1110 View Post
A picture would be great of your panel and disconnect. I know what the transfer switch looks like. Were you able to find the neutral bar on the transfer switch?
Yes, I was able to find the neutral bar on the transfer switch. I also think I know where the neutral bars are on the panel. There are 2 going down both sides, and then there is a ground bar on the right. Let me get a picture and upload it.

Good idea.
robmypro is offline   Reply With Quote
Old 08-31-2009, 07:03 PM   #18
Newbie
 
Join Date: Aug 2009
Posts: 15
Default

Generator Install - A few questions...


Quote:
Originally Posted by wirenut1110 View Post
A picture would be great of your panel and disconnect. I know what the transfer switch looks like.
Here are a few pictures. You can see the shutoff under the meter on the pole. I also took some outside pics so you can get an idea of the install. You can also see the 2 black wires and the one with the yellow stripe. They are about the same size (I was wrong).

Hope this helps, and thanks for the help!
Attached Thumbnails
Generator Install - A few questions...-generator-084.jpg   Generator Install - A few questions...-generator-086.jpg   Generator Install - A few questions...-generator-089.jpg  
robmypro is offline   Reply With Quote
Old 08-31-2009, 07:31 PM   #19
Electrical Contractor
 
wirenut1110's Avatar
 
Join Date: Apr 2008
Location: Chester, VA.
Posts: 1,046
Send a message via AIM to wirenut1110
Default

Generator Install - A few questions...


Do you know what year code your jurisdiction is under?

I would consult your AHJ to see if you can leave that 3 wire from the disconnect(pole) to the transfer switch and then pull a 4-wire from the switch to your panel. Then the grounding/bonding will need to take place in the switch. If not, you'll need a 4-wire from the disconnect to the switch and 4-wire to the panel.

Also, if you're under 08 code, the generator will need to be able to serve the entire load transferred. So you may have to add some load shedding. Hard to say, although a 20 KW should be able to handle it.

It looks like the neutral and grounds are bonded in your panel. Adding the switch, this would need to change.

I was thinking the meter and disconnect was attached to the house.

You may want to call a pro because there are rules that may or may not be in effect in your area and this will change significantly the way all these components come together.

I don't know where you are but someone here may be in your area and can shed some light on what you'll be able to do with the 3/4 wire issue.

Last edited by wirenut1110; 08-31-2009 at 07:34 PM.
wirenut1110 is offline   Reply With Quote
Old 08-31-2009, 07:41 PM   #20
Newbie
 
Join Date: Aug 2009
Posts: 15
Default

Generator Install - A few questions...


Quote:
Originally Posted by wirenut1110 View Post
Do you know what year code your jurisdiction is under?

I would consult your AHJ to see if you can leave that 3 wire from the disconnect(pole) to the transfer switch and then pull a 4-wire from the switch to your panel. Then the grounding/bonding will need to take place in the switch. If not, you'll need a 4-wire from the disconnect to the switch and 4-wire to the panel.

Also, if you're under 08 code, the generator will need to be able to serve the entire load transferred. So you may have to add some load shedding. Hard to say, although a 20 KW should be able to handle it.

It looks like the neutral and grounds are bonded in your panel. Adding the switch, this would need to change.

I was thinking the meter and disconnect was attached to the house.

You may want to call a pro because there are rules that may or may not be in effect in your area and this will change significantly the way all these components come together.

I don't know where you are but someone here may be in your area and can shed some light on what you'll be able to do with the 3/4 wire issue.
First, thanks a lot for all your help wirenut. After reading your replies I think it is safe to say I need a pro to install this thing. No problem and I really do appreciate all your help. I just wanted to see if this was something I could do, and that seems doubtful now. We are under 08 code, so it should be interesting.

Again, thank you very much. BTW, I am in Colorado (Jefferson County).
robmypro is offline   Reply With Quote
Old 08-31-2009, 07:50 PM   #21
Electrical Contractor
 
wirenut1110's Avatar
 
Join Date: Apr 2008
Location: Chester, VA.
Posts: 1,046
Send a message via AIM to wirenut1110
Default

Generator Install - A few questions...


No problem. Glad to be of assistance. Good generator you have also. I have about 15 of that model out there.

As an added note, if that window is operable (can be opened) the generator needs to be at least 5' away. These clearances are shown in your owner's and or installation manual.

And please obtain proper permits for this.

wirenut1110 is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help How to Wire Bathroom "Fan Heater Light Night-light" unit, and questions Tryvidy Electrical 9 06-18-2012 02:37 PM
How thick should my thinset be? yummy mummy Tiling, ceramics, marble 20 09-28-2009 12:36 PM
When to sand and other questions... PaintedSurface Painting 4 03-27-2009 09:13 PM
Laminate wood floor layout questions nathan.tran Flooring 4 08-30-2008 10:56 PM
tiling questions - in middle of install mwill Flooring 8 12-11-2007 05:06 PM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.