What I am looking to do? I'm looking to hookup a generator to my home in-case of a power outage to run the necessary items. I searched multiple forms and asked around and I'm getting different feedback.
Not surprising at all
I plan on purchasing a 9375 starting watts with 7500 running watts. It will have 120/240 Volt AC, 30 Amp (L14-30R). I'm going to install an outside receptacle which the generator will plug into, then I going to run a wire from the receptacle to my breaker box and connect that to a 30 Amp breaker. To meet code, I'm going to install an interlock kit system in which you MUST have the main power off in order to throw on the breaker for the generator. It is no more then a 25 foot run from the receptacle box to the breaker box.
My question is, what gauge wire do I need to run? Some sites are saying 10/4 and some are saying 8/4. What do I really need to run?
10/4 is rated 30 amps, so that's all you need your length of run isn't enough to cause an upsize in the cable awg. Do not use power cord from the power inlet box to the panel. Use house wiring like 10/3 with Grd NM-B (romex).
Once I have the wire ran back to the breaker, I connect the black and red to the breaker. Do the white and green go together to the neural bar?
If the panel is the service equipment (place where the first means of disconnect is located for the homes power) then you should see them connected together on the same bar. If there is anything different than that post a picture.