Originally Posted by Julius793
Ok now that I got home.... To prove my point that the frame of the generator MUST be bonded to neutral look at 250.34
250.30 is contrary to what your saying
250.30 - CAUTION: The neutral-to-ground connection for a separately derived system cannot be made at more than one location. To do so would create multiple neutral-to-ground connections, which produces multiple neutral current return paths to the grounded (neutral) conductor of power supply, which can create a fire, shock hazard as well as power quality problems from electromagnetic interference. See 250.6 and 250.142(A).
250.34 Generators-Portable and Vehicle-Mounted
(A) Portable Generators. The frame of a portable generator is not be required to be grounded to the earth if:
(1) The generator only supplies equipment or cord-and-plug-connected equipment through receptacles mounted on the generator, or both, and
(2) The metal parts of generator and the grounding terminals of the receptacles are bonded to the generator frame.
(B) Vehicle-Mounted Generators. The frame of a portable generator is not required to be grounded to the earth if:
(1) The generator frame is bonded to the vehicle frame.
(2) The generator only supplies equipment or cord-and-plug-connected equipment through receptacles mounted on the generator, or both, and
(3) The metal parts of generator and the grounding terminals of the receptacles are bonded to the generator frame.
FPN: Portable generators that supply fixed wiring systems must be grounded in accordance with 250.30 for separately derived systems if they supply a transfer switch that switches the neutral.
I am not using a transfer panel, I'm using an interlock directly back to the load center.