Generator Cord Length - Electrical - DIY Chatroom Home Improvement Forum
Old 06-21-2010, 03:45 PM   #1
What is the maximum length for a portable generator cord that is #10 gauge, 30 amp/240?
TNtmblweed is offline   Reply With Quote
Old 06-21-2010, 04:13 PM   #2
A 5% drop at 240v is 12v and 12v @ 30A is 0.4 ohm and this is 200' of two conductor copper #10.
Old 06-21-2010, 08:40 PM   #3
" Euro " electrician
frenchelectrican's Avatar
Yoyizit do your math again that number did not come up right and that is too long a distace for the 240 v 30 amp load and what more OP mention Generator cord and that useally rated at 25 amp not the 30 amp BTW.
The max distance is actally is 125 feet not the 200 feet because you did not took a account of the type of cord.
Merci,Marc
Old 06-21-2010, 09:38 PM   #4
Merci,Marc
Like they say in school, "Show your work." You already have my calcs.
Old 06-21-2010, 09:45 PM   #5
Ouais .,,,,
But next time you should take a account of the type of cord and the cord have diffrent ampacity than standard building wires that something you should be aware with it.
Most common genereator cord I have ran into they are SJOW or SJOOW one of the two and with 3 conductor 6.0mm have rated to 25 amp max if you have doubts I will snag up North Americian verison of this type of cord and it will have a ampacity chart you will go from there.
Merci,
Marc
Old 06-22-2010, 09:25 AM   #6
Ouais .,,,,
The French equivalent of "yeah"?
In that case it is 30/25 of 200' = 240' for a 5% drop for #10 AWG annealed copper at 20C if the table, my reasoning and my arithmetic is correct.
But, OP's are never wrong, by definition.
Last edited by Yoyizit; 06-22-2010 at 12:57 PM. Reason: arith right, reasoning not
Old 06-23-2010, 12:34 AM   #7
Yep you got it right it French word for Yeah.
The 20C is that for the ambemnt tempture ?? due I know the portable cord have diffrent tempture rating so let me dig up the info so give me a jour ou duex.
Merci.
Marc
Old 06-23-2010, 12:53 PM   #8
My automated online translator cartoon lady is teaching me French.
It's the temperature that the copper has a resistance of 1 ohm per thousand feet.
AC Temp drop over plenum run length BlueBSH HVAC 23 06-22-2010 08:10 AM
Hardwood Length...preference? JDeFuria Flooring 3 03-10-2009 05:38 PM
total effective length question drewhart HVAC 2 01-27-2009 08:46 PM
Maximum base board loop length Mike Warner HVAC 1 04-30-2008 11:48 PM
Pergola Unsupported Length wsuswim147 Building & Construction 2 04-08-2008 10:56 PM