-   -   generator battery trickle charger (http://www.diychatroom.com/f18/generator-battery-trickle-charger-80790/)
veretiL 09-07-2010 08:29 PM
I had a 715kva generator with 24vdc battery trickle charger and battery is getting dry most of the time , time and again i had to fill battery water and think the battery charger is not cut off when 24vdc is attain in battery, please could you help me identify the cause and also how to repair.
vsheetz 09-07-2010 10:20 PM
How long does it take to need water in the battery(s)?
frenchelectrican 09-08-2010 01:19 AM
715 KVA is pretty big unit { 715,000 watts }
Now with battery charging mode you should get a voltmeter and read in DC scale and with full charged batterys you should NOT be over 28 VDC anything over you will boil out the battery once you get into 30 volts the battery will boil out { dry out and it can be dangerous due the hyrodgen gaz }
How old the batteries are ? if more than 4 or 5 Years ditch them and get new one and please check the charger to make sure it is not overcharging if so you will either adjust the voltage on charger or replace it { if not adjustable charger }
You should get a full automatic charger with floating cutoff mode so when it get full charged it will turn the charger off until the battery voltage drop down a bit then kick it back on and it will cycle as need to.
With 715 KVA unit I know typically will have 2 or 4 size 8D or 4 Size 31 battery which it is correct for the unit this big.
And for stand by mode you should check the block heater as well { some will have thermostat as well }
If more question just let us know
I have deal quite few larger generators so I am famuair with it.
Oh do not run unloaded too long otherwise you will get wetstacking on diesel units { once the load is applied you may get afterburner on the exhaust or get hevey smoke for few minutes } Gaz unit do not have this issue but check the fuel system anyway.
Merci.
Marc
joed 09-08-2010 08:45 AM
Does your unit have a battery volt meter? The voltage should be between 26-27 volts when charging. It may go higher if has an equalization charge. Your charger might have some adjustments if it is boiling the batteries. Check the manual for the charger.
TimPa 09-08-2010 05:33 PM
trickle implies very low current, some milli-amps (< 1 amp anyway). if yours is truly a trickle charge, i doubt the batt electrolyte would evaporate. check with ammeter.
Speedy Petey 09-08-2010 06:51 PM
715kVA ??????? :eek:
Isn't this something a professional should work on?
What country are you in?