Generator And 3 Phase - Electrical - DIY Chatroom Home Improvement Forum
Old 06-17-2014, 03:19 AM   #1
Rewards Points: 192
Generator and 3 Phase
So I have a generator question. This is just for my knowledge.
If I have a building served by 3 phase 120/208 power, can I supplement that with a single phase 120/240 generator as long as any 208/240 loads can tolerate either voltage such as a range?
bcgfdc3 is offline   Reply With Quote
Old 06-17-2014, 06:39 AM   #2
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
It will work, obviously you won't be able to run anything that is 3 phase.... Probably involve a lot of moving circuit breakers around to ensure that all essential loads are being energized via two of the three legs that would be energized.
The Following 2 Users Say Thank You to stickboy1375 For This Useful Post:
bcgfdc3 (06-17-2014), Kpack (06-17-2014)
Old 06-17-2014, 02:23 PM   #3
Rewards Points: 1,832
It will work if the loads are 208 and 240 volt rated.
However, your ATS (automatic transfer switch) will have difficulties. Using a single phase transfer switch, it may not transfer back to utility after an outage or will always be transferring to emergency under normal conditions since a single phase ATS anticipates 240 volts nominal readings, not that of a 208 volt system. Only if the ATS is fully programmable its doable. Both the utility and generator high/low voltage limits will have to be adjusted individually in the ATS.
A 3 phase ATS may not work since it will always read one leg open from the generator.
Also of note, you will have to consider that resistive loads will draw more current on 240 than 208, so that to would need consideration.
Jump-start is offline   Reply With Quote
Old 06-17-2014, 02:28 PM   #4
Just popped into my mind, do you know anything about the generators alternator? A lot of commercial genets come with 12 lead alternators that can be reconfigured to a variety of connections. If this one can be configured from single phase to 3 phase all you problems are solved. Of course if the genset has that option to begin with.
The Following User Says Thank You to Jump-start For This Useful Post:
Old 06-17-2014, 02:54 PM   #5
Rewards Points: 192
Thanks for the replies. I was just curious. No actual generator in mind.