I am running ge sub panel to shed about 75 ft from main 200 amp box .in the sub panel there is only one bus bar for ground or neutral .Do i need another bar to split or can i use the one bar for ground and neutral coming from main box.and if i have to add is that all i have to do is buy bar and attach it to box.And i was gonna use 10/3 wire but i think im gonna use 6/3 just in case i add 220 to sub later.what do u think. heres pic of the box
tity04 is offline   Reply With Quote
Old 01-30-2008, 08:57 PM   #2
joed's Avatar
Rewards Points: 11,614
If there are no other metal paths( water line, phone line, gas line etc.) then you are permitted to use a three wire feeder and bond the neutral and ground. If other paths are present then you must unbond them.
Old 01-30-2008, 09:09 PM   #3
Electrician
Just buy a ground bar, the 2008 eliminates the 3 wire exception anyways... the panel will list the ground bar model #...
What type of 6-3? UF right? and you still need a disconnect at the shed also... you can install a breaker in that panel for the disconnect, or you can limit yourself to only 6 of the 8 breakers, and you need ground rods...
chris75 is offline   Reply With Quote
Old 01-31-2008, 06:44 AM   #4
i will be adding a satellite and phone line to shed.and what u are saying is i can add a main shut off breaker.and the uf does it have to be in conduit under ground
Old 01-31-2008, 11:42 AM   #5
A #6 conductor will only handle up to 70 AMPs at 75 feet.
If your sub-panel will be pulling up to 100 AMPs, you will need to upgrade your feed to a minimum of a #4 conductor. And as stated, the 2008 code requires a four-wire feed anyway. So, you will need a #4/3 with ground.
There is specially made cable for direct burial that does not require conduit with the exception of where it enters and leaves the ground.
PVC works well for this application, but check your local requirements.
Check out this website, it gives very clear instructions for setting up a sub-panel...WITH PICTURES!!
http://www.hammerzone.com/archives/e...1/overview.htm
Randell Tarin is offline   Reply With Quote
Old 01-31-2008, 01:32 PM   #6
Licensed Pro
Huh?
If he is using 6/3 UF, it is rated for 55A. He could upsize to 60 or use a 50.
Old 01-31-2008, 01:44 PM   #7
waiting for spring
arichard21's Avatar
Rewards Points: 150
arent 3awg required to pull 100amps?
arichard21 is offline   Reply With Quote
Old 01-31-2008, 02:19 PM   #8
The issue here is the amount of voltage drop over the distance of the run.
Check this out:
http://www.elec-toolbox.com/calculators/voltdrop.htm
http://www.csgnetwork.com/voltagedropcalc.html
For a run of 75 ft. @ 240 V and 100 AMPs, copper....the minimum wire size is #4. You didn't what the amperage for your panel was. Obviously, if it's less than 100 AMPs and you don't anticipate putting a larger load on it in the future, then go with a smaller size conductor.
Old 01-31-2008, 02:25 PM   #9
Licensed Pro
Randell: Take a look at the top of the page at that calculator site. See the part about not taking into account the minimum ampacity according to the NEC?
For a 100A circuit, the minimum size Cu conductor, assuming 75C terminations, is #3ga. Voltage drop should not be an issue at this distance.
Old 01-31-2008, 05:01 PM   #10
I stand corrected, sir.
Old 01-31-2008, 05:13 PM   #11
Electrician
FIrst off its a shed, I highly doubt he needs 100 amps, but personally do a load calculation so you know what you need... dont waste you money on copper you'll never use...
Old 01-31-2008, 05:18 PM   #12
I thought the same thing when I first did a shed next to my workshop. THEN, I bought a 220v stick welder. I'm now in the process of running a new feed and installing a new sub. Anticipate future needs or it could come back to bite you on the butt.
Old 02-25-2008, 11:09 PM   #13
im gonna use 8 gauge can i run 2 wire plus extra. 2 to hot bus and bare/other wire to neutral and for the ground run 8 ft ground rod with copper wire to a ground bar in sub-panel
Old 02-26-2008, 12:16 AM   #14
Rewards Points: 2,350
No.You need 4 wires. Others will chime in and say that there is anotherway, blah blah. But fact is, in a good installation, you need 4 wires: 2 hot, 1 neutral, 1 ground, and a ground rod.
InPhase277
Old 02-26-2008, 12:40 AM   #15
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
And a main disconnect....
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 08:37 AM
Multiple Sub Panel Installation Handyman2007 Electrical 26 12-31-2007 06:47 PM
Outdoor breaker panel questions lhoney2 Electrical 12 07-19-2007 06:44 PM
Splice in Neutral to Panel - OK or Not? allpraisebob Electrical 4 08-12-2006 06:54 AM
Adding new circuit breakers to 100 amp sub panel DrP Electrical 8 05-25-2006 11:05 PM