davsam 01-31-2011 12:47 PM
I tried to install the Timer yesterday to control my front porch light. It will only contiually flash on and off. I think I may have reversed to the black to black and the black to red wires. Any thoughts before I go back in.
clashley 01-31-2011 01:01 PM
This usually means that your neutral is not correctly wired to the switch. Unlike a single-pole switch, most digital timers require a neutral. You should have four connections on the timer:
  • hot lead (connect to incoming hot lead from the circuit breaker)
  • load lead (connect to outgoing hot lead to the light fixture)
  • neutral lead (connect to the neutral lead from the main panel and to the neutral lead from the light fixture)
  • ground lead (connect to the ground conductor from the main panel and to the light fixture).
It is possible that your original switch was on a switch loop and there is not a neutral conductor in the device box; if this is the case, you will need to pull a neutral conductor into the device box to make the digital timer work properly.
davsam 01-31-2011 03:28 PM
The smart switch is one of four switches in the box. Do I need to match the neutral wire with the actual switch, or will any one of the four wires work off of the bundle?