Garbage Disposal Circuit - Electrical - DIY Chatroom Home Improvement Forum
Old 06-27-2011, 06:06 PM   #1
Murdy's Avatar
Rewards Points: 37
Garbage disposal circuit
We are putting in 2 garbage disposals into 2 sinks relatively close to each other. Amp loads are 6.9 and 8.1 which equals 15, can I run them both off a single 20 amp circuit, or should I run dediated circuits, and if dedicated, I would assume 15 amp circuits would be ok. NEC is in effect; would one circuit satisfy code?
Thanks.
Murdy is offline   Reply With Quote
Old 06-27-2011, 07:59 PM   #2
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Thanks.
What are the horsepowers?
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 06-27-2011, 08:13 PM   #3
Murdy's Avatar
Rewards Points: 37
3/4 hp & 1/2 hp. They are Isinkerators, ones a 5 the other a 5xp.
Old 06-27-2011, 08:22 PM   #4
electures's Avatar
The 3/4HP will need a dedicated #14 circuit with a 35A breaker.
The 1/2HP will need a dedicated #14 cicuit with a 25A breaker.
They are motors and the requirements are specific. If you want I would be happy to provide the calculations for each motor.
Old 06-27-2011, 08:52 PM   #5
Master Electrician
Rewards Points: 3,864
That is TOTAL BS. You do not calculate residential appliance motor circuits using motor calculations.
Read NEC 430.6 in totality. Especially the exceptions.
brric is online now   Reply With Quote
The Following 5 Users Say Thank You to brric For This Useful Post:
Anti-wingnut (06-27-2011), HouseHelper (06-28-2011), McSteve (06-29-2011), mpoulton (06-27-2011), tweak (07-16-2011)
Old 06-27-2011, 09:16 PM   #6
Master Electrician
Thanks.
If you want to avoid problems and comply with the appliance instructions, run individual 15 amp circuits to each GD.
The Following 2 Users Say Thank You to brric For This Useful Post:
Anti-wingnut (06-27-2011), SD515 (06-27-2011)
Old 06-27-2011, 09:31 PM   #7
Rewards Points: 1,010
Thank you. I knew this was BS, but I was waiting for a real electrician to respond.
In my 30 years of industrial, commercial and multi-family construction, I have never seen a disposal protected with anything other than a 15 or 20 circuit breaker. The statement by our "Inspector" is ludicrous. Now you have residential wiring protected by a much bigger breaker than it safely should be.
This is the danger with so many of these sites, you get some "experts" who claim to be "State Electrical Inspectors" and some poor fool will listen to them
430.6 (A) (1) exception #3 - correct?
electures: You're a fool if as a inspector you can't tell someone how to safely wire a garbage disposal
Anti-wingnut is offline   Reply With Quote
The Following User Says Thank You to Anti-wingnut For This Useful Post:
gregzoll (07-09-2011)
Old 06-27-2011, 09:42 PM   #8
Semi-Pro Electro-Geek
Rewards Points: 2,938
Yeah, nobody sizes residential motor-based appliance circuits that way. Nor is there any good reason to. It wouldn't even be code compliant to use those breaker/conductor combinations if these disposals are cord-and-plug connected.
I'd install one 20A circuit for both of them. I'm not aware of any requirement that garbage disposals have a dedicated circuit. You can even add other receptacles on that circuit if you want to get more use out of it. However, you can't count it as one of the "small appliance circuits" required in a kitchen.
EDIT: brric makes a good point - the disposal instructions may call for a dedicated circuit to each.
mpoulton is offline   Reply With Quote
The Following User Says Thank You to mpoulton For This Useful Post:
Old 06-27-2011, 10:14 PM   #9
Murdy's Avatar
Rewards Points: 37
Thanks for all the input,
"It wouldn't even be code compliant to use those breaker/conductor combinations if these disposals are cord-and-plug connected"
That did make me scratch my head, but what the heck do I know.
And when in doubt, read the instructions.
My panel is getting a little crowded, and I though maybe I could get away with one 20 instead of 2 15's.
I appreciate eveyone's input.
Old 06-28-2011, 05:01 AM   #10
Electrician
SD515's Avatar
Rewards Points: 504
Do you know if your panel can accept twin/tandem breakers? Then it would only use one breaker slot.
Kyle
Old 06-28-2011, 05:18 AM   #11
I think in Canada we can put one garbage disposal on the same circuit as a dishwasher, but im not sure about putting 2 disposal's on the same circuit.
Haligonian is offline   Reply With Quote
Old 06-28-2011, 06:20 AM   #12
Lic Elect/Inspector/CPO
430.6 (A)(1) Exception No. 3: For a listed motor-operated appliance that is marked with both motor horsepower and full-load current, the motor full-load current marked on the nameplate of the appliance shall be used instead of the horsepower rating on the appliance nameplate to determine the ampacity or rating of the disconnecting means, the branch-circuit conductors, the controller, the branch-circuit short-circuit and ground-fault protection, and any separate overload protection.
They both could be run off a single 20 amp circuit.
NJMarine is offline   Reply With Quote
The Following User Says Thank You to NJMarine For This Useful Post:
frenchelectrican (06-29-2011)
Old 06-28-2011, 07:13 AM   #13
Murdy's Avatar
Rewards Points: 37
Thank you, NJMarine, for a definitive answer.
And, SD515, thanks for the input, my panel does accept the smaller breakers, and I will be using some. Still trying to conserve a circuit if I really don't need the extra one.
Thanks all.
Old 06-28-2011, 06:26 PM   #14
Electrician
SD515's Avatar
Rewards Points: 504
As a couple others have mentioned…run ‘em both off a 20A circuit, them only. Besides, when are you going to be using them at the same time? Even then, the duration probably wouldn’t be very long.
Kyle
Old 06-29-2011, 03:12 PM   #15
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,214
brric,
I think you teed off electures, he has not made another post since you called him on the OCPD requirements for the garbage disposers.
Coastal South Carolina
The Following User Says Thank You to rjniles For This Useful Post:
New Garbage disposal draining slowly. yoeye82 Plumbing 1 12-10-2010 03:40 PM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
Old garbage disposal question please help. linuxguy0481 Kitchen & Bath Remodeling 3 07-26-2009 10:03 PM
Garbage Disposal howard.wheaton Electrical 7 05-10-2009 06:36 AM
Garbage disposal muddog Electrical 3 06-07-2008 04:10 PM