#1 |
Garage Subpanel Wiring Question
I’m in the middle of wiring a 50amp subpanel in my attached garage for a welder and compressor (they won't be used at the same time so 50amp is sufficient). I have a couple of questions about using NM-B cable:
I plan to run about 30’ of 6-3 Romex (NM-B) cable along the floor joists in the basement from the main panel to an existing opening in the wall between the basement and garage. For physical protection going through the wall and into the subpanel, I’d like to remove the outer PVC jacket of the cable and run the three wires (plus ground) in ¾” EMT conduit for approx. 6’ (see pictures below). I’ll use an EMT to Romex fitting or bushing to transition. I’ve read that NM-B uses THHN wires, so is removing the PVC sheathing for a 6’ run like this ok to do? On the same subject, I also need to continue running #6 wire in a conduit from the subpanel to an outlet in the garage. I’d like to use the remaining NM-B cable since I’ll have some left over, but I don’t want to try to run cable through a conduit. It seems like I should be able to remove the PVC jacket and run the wires individually, but the wires aren’t individually labeled as being THHN, so I don’t know if this is ok to do. Everything will be inspected before the final connections are made, but any advice would be appreciated. Thanks ![]()
#2 |
I would put a junction box at the end of the conduit, with all of the appropriate clamps and fittings to admit the Romex cable and from there run the wire ends minus the sheath into the conduit.
The average homeowner who lost his house in the Oklahoma tornadoes should move for good and not rebuild. Too much complexity watchdogging the contractor. Too much a chance to be defrauded. |
#3 |
Licensed electrician
The conductors inside NM type cable are not labeled as to their insulation and cannot be stripped of the overall sheath and used in conduit as you propose. You can transition in a junction box to individual conductors or continue the conduit to the other panel.
Answers based on the National Electrical Code. Local amendments may apply. Check with your local building officials. |
#4 |
Thanks for the replies. What you said about the rating of the wires makes sense for the sub-panel to outlet run, but I just want to be clear about the run between the main panel and sub-panel.....it would be a continuous run with the 6' of individual wires clearly belonging to the cable. So you're saying that the wires that belong to the cable aren't rated for individual use? Thanks
#5 |
why not run a bigger conduit and not strip of the sheathing?
#6 | |
Garage Subpanel Wiring QuestionQuote:
#7 |
Why not run the cable direct to the panel. It does not look to be 'subject to damage' being that high up on the wall.
Do not PM with questions that can be asked in a forum. I will not respond. |
#8 |
I'd put a junction box right there at the end of that last 90 and transition to your romex right there. BTW, there is nothing saying that you cannot run the romex in conduit, either sleeving for protection (24" or less before derating) or through the entire run. You must calculate conduit fill by using the widest dimension of the romex. 6-3 is round anyway though.
#9 | ||
#10 |
This would not be Code compliant. The cable is listed as an assembly. Stripping the outer sheath removes the listing as the condictors are now unidentified as to type.
#11 |
Electrical Contractor
-KB Life is uncertain -- eat dessert first!! To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. |
| Display Modes | |
| Critique my wiring plan for my garage | tigereye | Electrical | 10 | 03-24-2009 10:55 PM |
| Legal to have subpanel in garage? | gante | Electrical | 36 | 03-13-2009 04:27 PM |
| Yup, another subpanel wiring question! | 737Pilot | Electrical | 3 | 12-17-2008 02:07 PM |
| subpanel question | Brik | Electrical | 2 | 11-30-2008 06:31 AM |
| Wiring new detached garage/studio | WShawn | Electrical | 4 | 07-21-2008 07:13 PM |