Originally Posted by rjniles
And not many electricians would use the term "outlet" when they were specifically talking about "receptacles". To an electricain an "outlet" has a different meaning.
Could have been worse and the OP had said plugs, that really drives me crazy.
You do not need to GFCI protect all the outlets in your garage, you need to protect the 120 volt receptacles.
I am bored, nit pick time:
210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel.
FPN: See 215.9 for ground-fault circuit-interrupter protection
for personnel on feeders.
(A) Dwelling Units. All
125-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
(1) through (8) shall have ground-fault circuit-interrupter
protection for personnel.
(2) Garages, and also accessory buildings that have a floor
located at or below grade level not intended as habitable
rooms and limited to storage areas, work areas,
and areas of similar use