Garage Heater - Electrical - DIY Chatroom Home Improvement Forum
Old 10-10-2011, 10:58 PM   #1
Rewards Points: 105
Garage heater
Want to run 220 out to my garage to use this heater http://www.ebay.com/itm/160522003371...84.m1423.l2648 just wanted to know if I can use 14g wire safely or should I use 12. Thanks.
gmbwrenchn is offline   Reply With Quote
Old 10-10-2011, 11:04 PM   #2
Rewards Points: 212
the most you are allowed to put on a 14 gauge is 15 amps. The heater says 20 amps. Therefore, you will need 12 gauge
bluebird5 is offline   Reply With Quote
Old 10-10-2011, 11:24 PM   #3
Electrical Contractor
jbfan's Avatar
Rewards Points: 254
Attached or detached garage?
Do you have a feed to the garage now?
Old 10-10-2011, 11:30 PM   #4
Rewards Points: 154
minimum #10
so 10/2 wire would be needed and a 30 amp breaker
awdblazer is offline   Reply With Quote
Old 10-11-2011, 01:07 AM   #5
Rewards Points: 212
Originally Posted by awdblazer View Post
minimum #10
The heater is 4000 watts which equals 16.67 amps. What would you want a 30 amp breaker on a 17 amp appliance?
Old 10-11-2011, 06:26 AM   #6
Licensed electrician
Rewards Points: 1,290
Here is why.
424.3 Branch Circuits.
(A) Branch-Circuit Requirements. Individual branch circuits
shall be permitted to supply any volt-ampere or wattage
rating of fixed electric space-heating equipment for
which they are rated.
Branch circuits supplying two or more outlets for fixed
electric space-heating equipment shall be rated 15, 20, 25,
or 30 amperes. In other than a dwelling unit, fixed infrared
heating equipment shall be permitted to be supplied from
branch circuits rated not over 50 amperes.
(B) Branch-Circuit Sizing. Fixed electric space-heating
equipment and motors shall be considered continuous load.
17 x 1.25 - 21.25. too much for a twenty amp circuit. Even using 16.67 x 1.25 = 20.8375.
bluebird5 (10-11-2011)
Old 10-11-2011, 09:48 AM   #7
Rewards Points: 724
also those heaters are illegal for permanent use, but most people don't care
carmusic is offline   Reply With Quote
Old 10-11-2011, 02:42 PM   #8
Semi-Pro Electro-Geek
Rewards Points: 2,902
Originally Posted by Jim Port View Post
(B) Branch-Circuit Sizing. Fixed electric space-heating equipment and motors shall be considered continuous load.
It's cord-and-plug connected, so not "fixed". I'd say it's a non-continuous load.
mpoulton is offline   Reply With Quote
Old 10-11-2011, 04:55 PM   #9
Rewards Points: 724
i agree with him, or else we could not plug 1500w portable space heater on 15A circuit (max 1440w for 80%). it is not a continuous load
i even use some 4800w ones on 20A breakers without problem for 15 years
Old 10-11-2011, 04:57 PM   #10
Rewards Points: 105
Detached garage. Yes there is a feed, but only 14/3
Old 10-11-2011, 04:59 PM   #11
Rewards Points: 105
Thanks for the replies.
Old 10-11-2011, 05:05 PM   #12
jbfan's Avatar
Rewards Points: 254
Since the garage has a feed, you can not run another feed.
You would need to increase the current feed and install a sub panel to use this heater.
Old 10-11-2011, 05:32 PM   #13
Missouri Bound's Avatar
With that feeder you will need a smaller heater.
water heater drip kdange1 Plumbing 6 10-29-2014 06:26 PM
Pilot on Williams millivolt wall heater goes out every 8 to 16 hours wornways HVAC 30 06-22-2011 04:29 PM
new double garage murray1426 Building & Construction 4 05-23-2009 02:11 PM
$59 "vent free" heater for garage? pcampbell HVAC 2 03-26-2008 03:24 PM