Forced Air Furnace Fan Setting Won't Work - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 07-23-2011, 06:01 PM   #16
Originally Posted by Missouri Bound View Post
On the second picture, there are screw terminals with smaller wires connected....I see a white and red wire.....any others connected to those screws?
Nope. Thanks in advance for everyone's help on this.
turkish777 is offline   Reply With Quote
Old 07-23-2011, 06:04 PM   #17
Missouri Bound's Avatar
With that connection, you have heat only, and fan on heat rise available. The fan switch cannot work as wired.
Old 07-23-2011, 06:09 PM   #18
Will the fan work if I connect the white wire to G on the thermostat?
Old 07-23-2011, 06:13 PM   #19
Unfortunately no. You need another wire to connect the terminals between the control board and the stat...if the furnace is wired for it. Can you see behind the terminal screws where (if anywhere) the wires go from the g terminal?
Old 07-23-2011, 06:18 PM   #20
I'm not following. Can I see the back of the thermostat where the G terminal is?
Old 07-23-2011, 06:20 PM   #21
NO...on the furnace....can you see behind the terminals on the board?
Old 07-23-2011, 06:23 PM   #22
Not really. It is screwed on.
Old 07-23-2011, 06:26 PM   #23
The only way to check it is to run a third wire to the thermostat....to the g terminal on the furnace to the g terminal on the stat.....there IS a g terminal on the furnace, right?
Old 07-23-2011, 06:46 PM   #24
Yes there is.
Old 07-23-2011, 06:48 PM   #25
Electrician
SD515's Avatar
Rewards Points: 504
There are 2 terminals on the furnace board that we can't see what they are. One should be 'G', the other probably is 'C'. (See picture)
Earlier you said your stat had a red and a blue wire hooked up, but the furnace has red and white hooked up. Has the cable been spliced? Maybe outside the furnace a couple feet up?
Kyle
Old 07-23-2011, 07:03 PM   #26
biggles's Avatar
go right to the fan motor wiring diagram on the motor fram see how many speed wires are showing heat is always LO or MED LO if you have HI speed wire that would be thru the stat from a relay in the furnace for cooling....the heat fan is controlled by that heat relay board....the stat has no control calling for fan your not wired.if you find a black HI speed wire and the white neutral coming from the motor i'll tell you how to control it with an add on relay that the stat can control
Old 07-23-2011, 07:07 PM   #27
Electrical Contractor
kbsparky's Avatar
Connect your spare wire to the "G" terminal on both the thermostat AND the furnace circuit board.
Then fan switch should now work on the thermostat.
-KB
Old 07-23-2011, 07:32 PM   #28
Electrician
SD515's Avatar
Rewards Points: 504
I'm thinking someone might have spliced the stat cable. OP said red and blue connected at the stat, but the photo posted clearly shows red and white connected to the board.
Kyle
Old 07-23-2011, 07:48 PM   #29
I suspect you are correct. The OP or somebody needs to wring out the wiring before wiring the thermostat properly is going to take place. I wonder if the wire can be pulled and replaced with the proper t-stat wire. It would be a good start.
Old 07-23-2011, 07:53 PM   #30
Maybe, I am not sure.
Goodman GMP100-3 Forced air furnace sylvia HVAC 23 12-18-2011 10:49 AM
Furnace Model # Feh-015-04 clicking but not turning on? haimei HVAC 1 12-14-2010 06:01 PM
Forced Hot Air Oil Furnace Issues? Power Vent? marcomjl HVAC 1 11-25-2010 10:48 AM
GOODMAN 100-3 Forced Air Furnace problem lindatbird HVAC 4 11-10-2010 09:55 PM
Adding a stand alone wood furnace to existing duct work vtboy51 HVAC 1 04-01-2009 03:19 PM