Floating neutral
After waiting 3 weeks for my appliance "service technician" to get my new oven to work (european with 3 wires -red black & yellow connected to red black & white for a 240 v service), He checks it with tester & says there is 120 to the red, 120 to the black but not 240 between them. "This is a problem in the electrical panel - there is a floating neutral - I only work on the appliance. Get an electrician." And he leaves. The breaker is new, the neutral appears properly attached - advice ?
#2 | |
Power Gen/RS Engineer
Floating neutralQuote:
I think he also works at my local HD.
The very existence of flamethrowers proves that some time, somewhere, someone said to themselves,"You know, I want to set those people over there on fire, but I'm just not close enough to get the job done." - George Carlin |
#3 |
Licensed Pro
Floating neutral
If you have 120V between the red and white and black and white, but do not have 240V between the red and black, then you have both hots on the same panel bus. You may have used a tandem breaker instead of a double pole breaker. A 240V double pole breaker should use two spaces in your panel. What type of panel do you have?
"Life is hard. Life is harder when you're stupid." John Wayne |
#4 |
Floating neutral Oh,Oh. It's a 2 pole breaker but it's on only one leg of the panel. All other spaces on the panel are full. What now?
#5 |
Floating neutral
Stan-
Please verify that this is a tandem breaker. It is basically two breakers in a single-space breaker body. If this is the case, find two adjacent circuits in the panel (i.e. same side, either left or right, immediately above/below one another) that are fed by normal, full-size 1-pole breakers. Relocate these two circuits to the 2 breakers in the tandem. Remove the now-vacant single pole breakers and install a double, common trip breaker with the proper amperage rating. Make sure that the rating of the tandem is equivalent to that of the two 1-pole breakers. Jim
#6 |
Floating neutral
Thanks Big Jimmy! Worked like a charm-got my 240v & a working oven. Mucho appreciation this Cinco de Mayo!
#7 |
Floating neutral
Glad it worked. Whydontcha email me a plate of nacho's?!
#8 |
Advice worth 2 cents!
Floating neutral
Now that was a nice happy ending!
But can you imagine the "service technician" not knowing that? Not willing to give the panel a glance?....pretty lame to me... - pete
---pete |
| Display Modes | |
| Problem with Neutral Connection | kbrigham | Electrical | 4 | 03-11-2008 08:00 PM |
| 12v diff between ground and neutral at panel | am9518 | Electrical | 7 | 02-25-2008 07:28 PM |
| Sub panel grounding | sluggermike | Electrical | 27 | 11-11-2007 02:23 AM |
| Suspected open/loose service neutral | mrtomwj | Electrical | 5 | 09-28-2006 09:46 AM |
| Splice in Neutral to Panel - OK or Not? | allpraisebob | Electrical | 4 | 08-12-2006 06:54 AM |