Feed To Tractor Storage - Electrical - DIY Chatroom Home Improvement Forum
Old 08-22-2012, 07:12 PM   #1
Feed to tractor storage
Brother-in-law wants me to help him figure out what wiring to run to his new tractor storage. Right now he has a 200 amp feed and panel to his workshop and he wants to run power to tractor storage for a few plug-ins, lights and probably a 50 amp circut for a 220volt welder to do repairs. The new storage will be 145 feet away from existing panel and he wants to run underground in conduit.
Sorry hit the wrong key.
What cable do we need to run and what amp breaker do we need to use for a feed? Know will be running 4 wires but need to know size and feed breaker amperage recommended.
Russell is offline   Reply With Quote
Old 08-22-2012, 07:47 PM   #2
Master Electrician
he'll need a subpanel. sounds like a 100A one, should be good with a number three feeder assuming draw with welder running will be around 70a.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 08-22-2012, 07:56 PM   #3
Thanks, planned on adding a subpanel in new tractor storage. Was needing to know what size breaker to put in workshop panel to feed the subpanel and what size wire (and type ) to run to the new shop.
Thanks!!!!
Old 08-22-2012, 08:03 PM   #4
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
1 1/2 PVC
3 #3's CU, 1 #8 CU (ground)
2 Pole 90A breaker
2 ground rods (Bond to water also, if present)
Remove neutral/ground bonding jumper in panel
Old 08-22-2012, 08:13 PM   #5
Thank you very much !!!!!!!! Extremely helpful!! The 2 ground rods go where? Both at new storage connected to ground at the panel?
Thanks again!!!!!
Old 08-22-2012, 08:48 PM   #6
Can cu 3-3-3-5 Ser be used underground in conduit?
Old 08-22-2012, 09:12 PM   #7
Licensed electrician
Rewards Points: 1,622
SER cannot be used underground.
andrew79 (08-22-2012)
Old 08-22-2012, 09:27 PM   #8
Master Electrician
i thought i remembered that but i didn't want to look like an idiot asking
Old 08-22-2012, 09:50 PM   #9
kevinp22's Avatar
Rewards Points: 252
[quote=Russell;994312]The 2 ground rods go where? Both at new storage connected to ground at the panel?
/quote]
Drive 2 ground rods at/near the subpanel at the tractor storage building (you can get away with 1 if resitance is 25 ohms or less but most people just drive 2). rods must be at least 6 feet apart
Use #6 copper (or larger) wire to connect the rods to the panel. you can use #8 but it has to be protected above ground (easier to use #6 in my opinion) Connect the wire to the ground bus of the subpanel (as mentioned, the neutral needs to be isolated from ground. the #8 ground wire going back to the workshop also gets connected to this bus). wire can be solid or stranded and is usually bare.
Rods must be at least 8 feet long and 5/8 in diameter (listed rods can be 1/2). Connect the copper wire with ground rod clamps approved for direct burial. Wire must be continuous from panel to first rod. Its easier and better (in my opinion) if the wire is continuous to both rods.
I use a sledgehammer to drive my many rods but pros often use a rotary hammer.
kevinp22 is offline   Reply With Quote
Old 08-23-2012, 10:01 AM   #10
Thanks to all for the great answers!!!!
Have a great day
Detached Garage Subpanel + Generator Back Feed insaneirish Electrical 3 09-06-2011 02:09 AM
Two Condos - One Feed mortym Plumbing 4 07-05-2011 07:43 AM
Multiple separate switched from common feed tpagel Electrical 2 07-03-2011 04:47 PM
feed to subpanel question JCA1 Electrical 1 03-11-2008 08:16 PM
RSS Feed Help DeeTee Site Help and Suggestions 1 08-30-2007 07:39 PM
