Feed To Sub-panel Questions ? - Electrical - DIY Chatroom Home Improvement Forum
Old 09-16-2008, 11:57 AM   #1
Feed to sub-panel questions ?
I'm planning on installing a sub-panel in my basement workshop to add 120 and 240 volt circuits in the shop. The sub-panel will be situated within 3 feet of the existing panelboard, but on an adjacent wall. I will feed the sub-panel through a 60 amp 2-pole breaker and use 6/3 plus ground NM cable run up, then over through a few ceiling joists, then down to the sub-panel (about a 12 foot run max).
My questions below concern the feed between the main and sub panels:
1. What diameter EMT conduit or FMC do you estimate I'll need to protect the 6/3 plus ground NM cable on the short run along the concrete basement wall from the joists to the panel? Any preference as to EMT vs. FMC?
2. Is plain NM 6/3 plus ground acceptable, or should I use NMC (if I can find it)? My basement is dry.
3. As an alternative, I was considering running 4 gauge THHN/THHW wire within FMC (3 wires plus ground) for the run, pending cost differences. This would allow me to go with a larger 80 amp feeding breaker. Does this sound acceptable? What gauge ground wire would I need?
Thanks for you help.
Dave
WoodworkerDave is offline   Reply With Quote
Old 09-16-2008, 06:25 PM   #2
Electrician
I wouldn't install anything to protect the NM. but thats just me... check this out...
chris75 is offline   Reply With Quote
Old 09-16-2008, 09:25 PM   #3
Idiot Emeritus
Rewards Points: 1,476
The breaker size feeding the sub-panel depends on what you're powering.
In a woodworking shop, usually only one tool is running at any given time, except for a dust system. A 60 amp breaker will reliably start a 5HP motor, while a 1HP dust collector is running, but not much more, assuming both are 240 volt.
Unless it's in an area where it might get clobbered, I wouldn't bother to protect the NM feeder. If it does get smashed, the 60 amp breaker will trip.
If possible, I'd put the lights on a separate circuit fed from the main panel. That way if the feeder to the sub trips, you won't be in the dark.
Rob
micromind is offline   Reply With Quote
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 10:27 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM
Pool Sub Panel wire / conduit questions Al the Diy guy Electrical 23 02-03-2008 02:32 PM
Outdoor breaker panel questions lhoney2 Electrical 12 07-19-2007 05:44 PM
Main/Sub/Garage Gen Backup Questions crecore Electrical 9 04-17-2006 06:31 PM