-   -   Feed to sub-panel questions ? (http://www.diychatroom.com/f18/feed-sub-panel-questions-26906/)
WoodworkerDave 09-16-2008 12:57 PM
I'm planning on installing a sub-panel in my basement workshop to add 120 and 240 volt circuits in the shop. The sub-panel will be situated within 3 feet of the existing panelboard, but on an adjacent wall. I will feed the sub-panel through a 60 amp 2-pole breaker and use 6/3 plus ground NM cable run up, then over through a few ceiling joists, then down to the sub-panel (about a 12 foot run max).
My questions below concern the feed between the main and sub panels:
1. What diameter EMT conduit or FMC do you estimate I'll need to protect the 6/3 plus ground NM cable on the short run along the concrete basement wall from the joists to the panel? Any preference as to EMT vs. FMC?
2. Is plain NM 6/3 plus ground acceptable, or should I use NMC (if I can find it)? My basement is dry.
3. As an alternative, I was considering running 4 gauge THHN/THHW wire within FMC (3 wires plus ground) for the run, pending cost differences. This would allow me to go with a larger 80 amp feeding breaker. Does this sound acceptable? What gauge ground wire would I need?
Thanks for you help.
Dave
chris75 09-16-2008 07:25 PM
I wouldn't install anything to protect the NM. but thats just me... check this out...
http://i171.photobucket.com/albums/u...ember07126.jpg
micromind 09-16-2008 10:25 PM
The breaker size feeding the sub-panel depends on what you're powering.
In a woodworking shop, usually only one tool is running at any given time, except for a dust system. A 60 amp breaker will reliably start a 5HP motor, while a 1HP dust collector is running, but not much more, assuming both are 240 volt.
Unless it's in an area where it might get clobbered, I wouldn't bother to protect the NM feeder. If it does get smashed, the 60 amp breaker will trip.
If possible, I'd put the lights on a separate circuit fed from the main panel. That way if the feeder to the sub trips, you won't be in the dark.
Rob