Farm Wiring - Electrical - DIY Chatroom Home Improvement Forum
Old 01-18-2012, 01:35 PM   #1
Farm wiring
I have some questions about the wiring I did when I upgraded a sub panel in a friends barn.
What was there before was a forty year old rusty Wadsworth panel. The barn is just fed with a 40 amp feed. It is fed with three wires (two hots and a neutral) from the main panel. The wires directly buried in the ground and is not rated for that. (Was existing when I got there). Off this 40 amp sub panel another building is fed via a 20 amp breaker.
My question is, with the three wire feed, is it ok to have the neutrals and grounds on the same bus bars? I added a ground wire and ground rod, the barn did not have that when I started.
This picture is a year old and before I finished everything.
http://smg.photobucket.com/albums/v2...t=100_0789.jpg
This is the main panel for the farm
http://smg.photobucket.com/albums/v2...t=100_0821.jpg
OldRedFord is offline   Reply With Quote
Old 01-18-2012, 01:44 PM   #2
Julius793's Avatar
then rip them out and start over!
Electricity will kill you if you give it a chance
Julius793 is offline   Reply With Quote
Old 01-18-2012, 05:18 PM   #3
joed's Avatar
Rewards Points: 12,918
With a three wire feed you must bond the ground and neutral even with ground rods.
Old 01-18-2012, 05:37 PM   #4
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Another person who confuses grounding with bonding.....
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 01-18-2012, 10:36 PM   #5
joed's Avatar
Straighten me out then please.
Old 01-19-2012, 06:53 AM   #6
Rewards Points: 1,514
With the existing 3 wire feed to the outbuilding you should bond branch circuit grounded conductors to equipment grounding conductors to grounding electrode (grounding electrode conductor is attached to the latter) in the panel out there.
Should the existing feed between the buildings fail, for example subterranean animals chewed the insulation and then the conductors corroded or shorted, or you need more ampacity, the new cable needs 4 conductors (for 120/240 volt) and you then unbond the neutrals and grounds at the outbuilding. For this reason it is suggested that you use separate terminal strips (bus bars) from the git go in the subpanel for neutrals and grounds. Neutral and ground would be bonded typically using bus bar screws that dug into the subpanel back, or a jumper wire between the busses sized for the one largest branch circuit EGC in the subpanel.
Hint: If A is bonded to B and B is bonded to C ergo A is bonded to C.
Old 01-19-2012, 07:37 AM   #7
Rewards Points: 3,256
I believe he was referring to the OP.
zappa is offline   Reply With Quote
Attic wiring - ceiling lighting uses 14/2 cable without ground darlingm Electrical 3 11-29-2011 09:01 AM
Backyard wiring questions MikeInDetroit Electrical 1 11-02-2011 09:46 AM
Landscape wiring question: GFCI and Breaker Amp MikeInDetroit Electrical 0 11-02-2011 09:43 AM
Cloth Wiring - Replace? JessicaGus Electrical 9 09-23-2009 06:45 PM
Knob & Tube wiring - How concerned should we be? hotdiggitydog Electrical 6 04-11-2006 07:52 PM