A.f.c.i. Meets L.V.lighting Panel. - Electrical - DIY Chatroom Home Improvement Forum
Old 12-07-2008, 09:52 PM   #1
a.f.c.i. meets L.V.lighting panel.
courious if anyone has dealt with arc fault circuits feeding, lighting panel ,dimming/relay modules.does anyone know what code says about lighting and a.f.c.i.?required?
eslbl is offline   Reply With Quote
Old 12-08-2008, 06:15 AM   #2
dSilanskas's Avatar
I'v been using Arc faults on my L/V panels for about six months now. Havne't run into any issues yet
dSilanskas is offline   Reply With Quote
Old 12-08-2008, 07:53 AM   #3
Registered User
Termite's Avatar
The code requires AFCI protection for all lighting and receptacles in sleeping areas. The 2008 NEC requires AFCI for all circuits in a home 20amps or less. I don't imagine LV lighting gets you out of the requirement.
Old 12-08-2008, 08:19 PM   #4
dSilanskas's Avatar
If your asking if you will have a problem with the AFCI and LV panel no you wont. If everything is wiring correctly you will be fine
Old 12-08-2008, 08:35 PM   #5
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
If this is in a kitchen or bath, would it only be required to have GFCI protection or are they now requiring ARC fault even for kitchen and bath in 2008?
Jamie
jamiedolan is offline   Reply With Quote
Old 12-08-2008, 09:42 PM   #6
Registered User
Termite's Avatar
Jamie I'm not sure because I'm enforcing the 2002 NEC in my behind-the-times jurisdiction.
I don't see why the kitchen and bath receptacle circuits wouldn't be required to be AFCI protected though. GFCI protection can be obtained at the devices. Most electricians don't use GFCI breakers at those locations anyway, just because of the inconvenience of having to go to the panel to reset (that equals callbacks for builders). It is much more homeowner friendly to use GFCI devices in the bath and kitchen.
Adding a second Electric sub panel TW Lucas Electrical 9 10-05-2008 02:37 AM
Melted Service Entrance Wire in Panel theatretch85 Electrical 13 08-22-2008 10:37 AM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 10:27 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 07:37 AM