Hey guys, I have this ground wire (I think it is a ground wire) sticking up from out of my pool. A guy offered to cut this for me and hide it but it seems I can do that myself. Does every pool just have a ground wire going around it to protect it from shock or something? Can I just cut this and hide it? Thanks!
it's there for a reason how about burying it under those wood chip or stones things...stick it in the ground slam a rod into the ground and secure it to that...unless somebody else kicks in on it
Was there some kind of equipment there previously? A heater, ladder, diving board, filter, etc.? It's rather odd to have a random bonding wire sicking out of the ground.
No idea what it is, I don't think there was anything there. I'm just going to bury it that seems VERY logical, but did not cross my mind. Thanks for replying to my thread guys, I think you saved me from bozo'ing myself once again.
I was trying to look up what this bonding grid is, I still am unclear. Am I right when I put it simply that it grounds metal within 5 feet of the pool? Kind of like a ground wire you use in a ceiling fan or electrical outlet?
http://www.mikeholt.com/mojonewsarchive/NEC-HTML/HTML/SwimmingPoolInstallations~20021227.htm
Quote below from this link above Author's Comment: Bonding is required for diving structures, sliding glass door frames, windows , fences, screen enclosures, heater equipment, and the metal cases of electrical equipment, such as the blower, chlorinator, etc. located within 5 ft of the water’s edge. (C) Common Bonding Grid. The metallic parts of a pool, outdoor spa or hot tub specified in 680.26(B) shall be electrically bonded to a common bonding grid by a solid conductor not smaller than 8 AWG. The termination of the bonding conductor shall be made by exothermic welding, or clamps labeled (listed) as being suitable for the purpose. The common bonding grid can consist of any of the following: Figure 680-20 un680-20 680-26C.cdr
It doesn't just ground it. Most of the metal around a pool is literally grounded already - it's in contact with the earth or the water. This is insufficient to ensure that it remains at "ground" potential, because the earth has fairly high resistance. The bonding grid connects all metal objects and equipment, the reinforced concrete around the pool, and the pool water itself, together with copper wire. This ensures that all of the bonded parts stay at the same voltage. That way there is no possibility that you can be shocked by touching any of those things while in or around the pool.
Basically. All metal parts of/around a pool get bonded to the supply circuit EGC. Gives any possible stray currents a place to safely go. A low impedance path like a receptacle, etc.
If you check the pool equipment, you should see a similar wire bonded to the outside of your pool pump, and possibly other equipment there. It is part of the equipotential bonding system that protects anyone in the pool from stray currents. If that wire is just hanging loose, it might be wise to connect it back to the pool equipment with 8 gauge copper wire (green).
since it already looks like it has been compromised I would make sure that the bonding from the metal parts such as ladder, rails, wet niche are still connected together and going back to motor.
I easily buried it and found that the wire is likely grounded back to the pool pump since the wire looks the same there.
Related Threads
DIY Home Improvement Forum
3.1M posts
319.6K members
Since 2003