Old 07-03-2008, 04:28 PM   #16
liscenced electrician
Enhancing existing wiring to detached garage
what do you mean. I know you know what it says, since youve been refferencing it, but....
225.39 says all disconnects for feeders must be 60A.
Originally Posted by chris75 View Post
Section 225.39 (D)
In other words, you can easily run #12 feeder to the garage, but your disconnect would have to be rated at 60 amps.
So youd be saying to run a number 12 for a feeder. And use a 60 amp breaker to disconnect that feeder.
jimmy21 is offline   Reply With Quote
Old 07-03-2008, 04:54 PM   #17
Electrician
The disconnect is at the detached structure. So in a nutshell, I can easily run a 12-3 feeder out of the house panel with 20a OCP, when I get to the detached structure, I install a MIN. 60amp disconnect ( weather it be a main breaker panel or some other Suitable for Service Equipment disconnect) and be on my marry way.
Hope this helps!
chris75 is offline   Reply With Quote
Old 07-03-2008, 05:55 PM   #18
if you did that you feeder wouldn't have a 60 amp disconnect. It would have a 60 amp disconnect downstream from it. You are misinterpreting the code. Flat out. Its saying the 60 amp disconnect must disconnect the feeder. The way your reading it makes no sense at all. Why would the NEC care what size breaker you have downstream of what its talking about protecting?
You can do what you saying legally, if its attached garage, where 225.39 would have nothing to do with it. And further more if its not getting inspected, who gives a crap as long as its safe
Old 07-03-2008, 05:57 PM   #19
That's great that this thread inspired a spirited discussion, but I think from the fourth post and beyond it was way above my head and far more information that I was seeking.
Remember I closed my OP with this:
Originally Posted by justinperkins View Post
It's an old house and I'm trying to make do with what I have for the time being until we have enough money to have the house rewired and a new panel installed.
Basically I was trying to determine if my existing circuit is maxed out or if it is OK to add the additional fluorescents I am referring to. Also, in the case that it is maxed out, can I simply add a subpanel in the garage, add two breakers and then feed my fluorescents from one breaker and the outlets from another.
wrt to adding a ground spike at the shop, I would love to do that since it would give my shop grounded outlets (remember my house is not grounded).
btw, nothing is getting inspected, I just want it safe.
justinperkins is offline   Reply With Quote
Old 07-03-2008, 06:21 PM   #20
Licensed Pro
Having a ground rod has nothing to do with having grounded outlets. The ground of the receptacles are connected to the panel ground (main or sub) which are ultimately bonded to the neutral (at the main service). A ground rod provides protection from lightning and high voltage. It does not provide short circuit protection.
Old 07-03-2008, 06:29 PM   #21
General Contractor
MacRoadie's Avatar
Hope this helps!
Ok, now I'm confused. If you install a 20a breaker at the main panel, then run your 12-3 feeders to the garage, then install a 60a disconnect at the garage end, what purpose does the disconnect serve? If your overcurrent protection is determined by the 20a breaker at the service panel, why would the disconnect be rated at 40a greater than the overcurrent protection will allow?
MacRoadie is offline   Reply With Quote
Old 07-03-2008, 07:00 PM   #22
the purpose of the disconnect would be so you can manually shut off power from inside the garage. It would be safe, but not up to code if it were a detatched garage. You would be required to run at least 2 #6s and an #8 nuetral, protected by a 60a breaker with driven ground rods.
The purpose for ground rods, is to make sure the ground and your grounding system in your house, along with your water pipes, all have the same potential.
Old 07-03-2008, 07:08 PM   #23
General Contractor
MacRoadie's Avatar
I understand the need for the disconnect, and the purpose of the ground rod (wasn't questioning the ground). The 2 #6's, 60a breaker, etc. makes much more sense to me than a 20a and 12-3.
Old 07-03-2008, 10:33 PM   #24
Electrician
The disconnect at the outbuilding is not protecting anything, its a disconnect and the NEC REQUIRES it to be rated at 60 amps. Flat out.. I dont know why you find this so hard to believe. and I already asked you to PM me if you have any questions on this instead of turning this thread into something its not.
are you even an electrician?
Old 07-03-2008, 10:37 PM   #25
Electrician
Its a DISCONNECT not overload protection, the nec wants it rated at 60 amps, plain and simple...
Old 07-03-2008, 10:39 PM   #26
Floor Sweeper
Why not?
Where in the NEC does it say that I cannot run, say a 10/3 feeder to a detached structure? (It doesn't!)
2008 NEC requires a seperate nuetral and ground when you run a feeder. Read 250.32.
No, the ground rods have nothing to do with keeping anything at the same potential. Bonding everything together keeps things at the same potential.
Ground rods are supposed to guard against overvoltage, such as lightning and such.
junkcollector is offline   Reply With Quote
Old 07-03-2008, 10:41 PM   #27
Electrician
If you dont believe me, then take that statement over to Mike Holts Forum and post that question. I dont know where your reading that the required DISCONNECT must be fed by a certain size wire?
Old 07-04-2008, 11:00 AM   #28
Electrician
Jimmy, have you seen the light yet?
Old 07-04-2008, 01:54 PM   #29
Jeez, I was going to ask some questions about my own sub panel project, but I'm a little scared to now!
white29 is offline   Reply With Quote
Old 07-04-2008, 02:12 PM   #30
Electrician
I wanted to finish this by PM, its was an nec issue, but please, do not feel scared to ask a question, this thread got hi-jacked and it happens from time to time.
Tags
breaker, electrical, garage
Mold in detached garage jkrodger Building & Construction 15 05-01-2009 02:46 PM
Grounding for detached all-metal garage geeswanie Electrical 3 07-03-2008 08:31 AM
Detached Garage Sub Panel Grounding Q integlikewhoa Electrical 13 01-01-2008 07:22 AM
detached garage Kapt Electrical 12 01-17-2007 09:37 AM
Framing a carport on a detached garage nomagic Carpentry 3 05-04-2006 11:43 PM