EMT And WIRE Size - 100 Amp Sub Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 05-16-2010, 12:26 AM   #1
100 amp sub panel
i am currently installing a two 125 amp sub panel and it is terminal lug only .
this two panel will receive power from 200 amp 2 gang meter with two 100 amp main breaker. my question is will terminal lug panel o.k to use or should i use a su panel with a 100 amp main breaker. is 1 1/2 emt o.k to use from sub panel to main panel.
balansaj is offline   Reply With Quote
Old 05-16-2010, 09:03 AM   #2
Sparkaholic
Rewards Points: 150
Send a message via Yahoo to sparks1up
If you have main breakers at the meter for each of the panels you don't need a main breaker in the panel.
1-1/2" EMT conduit is fine you could even run 1-1/4"
Answers based on the mood I am in when you ask!
sparks1up is offline   Reply With Quote
Old 05-16-2010, 02:28 PM   #3
Master Electrician
Rewards Points: 3,750
Main lug panel is okay unless it is in another building.
brric is offline   Reply With Quote
Old 05-18-2010, 01:33 AM   #4
EMT and WIRE size - 100 amp sub panel
I have a 200 amp service main panel with 2 meters and 2 100 amp DP breakers. I will be installing 2 100 amp sub panel and both are only 25 ft. away from the main. My questions are ; 1) what size of wire should I use?
2) Can I run the ground wire in the conduit along with the other 3 wires?
3) If so , what size of ground wire ? 4) Do I still need to ground or bound the sub panel to a water pipe. 5) What size of EMT should I run ?
I will highly apprecite any response. THANK YOU.
Old 05-18-2010, 12:21 PM   #5
Rewards Points: 80
1) 3-#3 copper for 100 amp sub panel. 1-#8 EGC.
2) The ground wire EGC must be run with the feeder conductors. So you will be pulling 4 wires H-H-N-G. #8 Ground wire is sufficient. Minimum.
3) No, the EGC is connected to the grounding/neutral buss bar in the main panels. Bonding only occurs at the service. There are exceptions, but not in your case.
4) I would run at least 1-1/2". You could use a 1" and be compliant, but its way to small in my opinion. Use 1.5 or 2.0 inch.
Old 05-18-2010, 01:22 PM   #6
Master Electrician
1.25 " EMT is large enough and would not require an equipment grounding conductor but I would install one anyway.
Old 05-18-2010, 04:17 PM   #7
Rewards Points: 80
If he was extending the service, (he is not) he would not require the EGC, he would require a GEC for both new service panels.
It sounds like he is running two 100 amp feeders 25' from two 100 amp breakers in a meter main. If he was extending the service with lug adapters at the meter then I would agree with your statement regarding the EGC. These are not services,they are feeders.
Why do you say he does not require the EGC. I am asking. Thanks John