EMT Conduit/Junction/Grounding - Electrical - DIY Chatroom Home Improvement Forum
Old 09-15-2011, 01:02 PM   #1
Rewards Points: 33
I am running 2x 20Amp circuits inside 1/2" EMT conduit. Base on a calculation, I should be able to run 4 circuits with #12 THHN wires (4 Hots, 4 Neutral, 1 ground). I plan to run 1 insulated ground wire.
My questions are:
1) Do I have to ground every metal junction box?
2) Is there any limit in length of EMT conduit between junction boxes?
3) If I use 1 ground wire, can I use #12 or I will need a bigger since this will be a shared ground.
4) Do I need to color coded different hot wires? Or it is ok just to tape wires at the end?
5) Can I wrap each circuit together with electrical tape? (E.g. wrap it every 3-4 feets).
TIA
cfreak is offline   Reply With Quote
Old 09-15-2011, 01:15 PM   #2
Code05's Avatar
Rewards Points: 1,104
If there is an wire EGC/ground, yes.
No
EGC/ground wires needs not be larger than hots.
Unless you have more than 1 supply, no identification necessary.
Why. MWBC need only be grouped at panel.
Code05 is offline   Reply With Quote
The Following User Says Thank You to Code05 For This Useful Post:
cfreak (09-15-2011)
Old 09-15-2011, 02:13 PM   #3
Rewards Points: 1,002
You do know that you can use the EMT as your ground, and not run a ground wire inside the conduit?
Anti-wingnut is offline   Reply With Quote
The Following User Says Thank You to Anti-wingnut For This Useful Post:
cfreak (09-15-2011)
Old 09-15-2011, 03:28 PM   #4
Rewards Points: 33
Yes, I read about that in one thread but there are negative opinions about doing so.
Just wondering, what are the different/limitation when using EMT, bare cooper, insulated EGC/ground?
Thanks,
Old 09-15-2011, 03:37 PM   #5
Code05's Avatar
Thanks,
All three are legal.
cfreak (09-15-2011)
Old 09-15-2011, 04:21 PM   #6
Electrician
Rewards Points: 792
I do it every day, and would not hesitate to do it my own house. Why are you pulling 4 neutrals, if you use multi wire branch circuits you can get away with two neutrals.
darren is offline   Reply With Quote
Old 09-16-2011, 07:23 AM   #7
Chaos Engineer
Big N8's Avatar
Rewards Points: 152
I agree you can take three of those wires out of that conduit and be 100% safe and 100% to code (unless some silly local code comes into play)
Big N8 is offline   Reply With Quote
Old 09-16-2011, 07:27 AM   #8
Code05's Avatar
MWBC are rapidly disappearing in most residential in the US because of AFCI protection for many 120v circuits. Currently the kitchen, bath, laundry, garage, attic, unfinished basements and exterior outlets are exempt, but who knows for how long.
Here is our code section:
210.12 Arc-Fault Circuit-Interrupter Protection.
(A) Definition: Arc-Fault Circuit Interrupter (AFCI). A
device intended to provide protection from the effects of
arc faults by recognizing characteristics unique to arcing
and by functioning to de-energize the circuit when an arc
fault is detected.
(B) Dwelling Units. All 120-volt, single phase, 15- and
20-ampere branch circuits supplying outlets installed in
dwelling unit family rooms, dining rooms, living rooms,
parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall be
protected by a listed arc-fault circuit interrupter,
combination-type, installed to provide protection of the
branch circuit.
Old 09-16-2011, 03:21 PM   #9
Electrician
Rewards Points: 792
Were lucky here then, we only have to do bedrooms on arc faults.
I didn't consider the circuits in the pipe may have been arc fault but if they are you will need seperate neutrals.