EMT Conduit - Electrical - DIY Chatroom Home Improvement Forum
Old 01-29-2009, 04:11 AM   #1
EMT Conduit
When can EMT conduit be used outdoors? I guess I always thought that it had to be fairly well protected from moisture, but I've noticed a lot of it run on outside walls, fences, etc. (commercial, professionally done work) where it's pretty much exposed to rain, sprinklers, etc.
Of course, I've also seen it run underground, but I assume NOT by a real electrician .
Gary
garyoutwest is offline   Reply With Quote
Old 01-29-2009, 05:58 AM   #2
Remodeling Contractor
EMT can be used outside using rain tight fittings where above ground and not subject to extreme physical damage. GRC is needed in that case and PVC underground.
Old 01-29-2009, 10:41 AM   #3
We get 7" of annual rainfal so anywhere outside/above ground is good here.
220/221 is offline   Reply With Quote
Old 01-29-2009, 10:56 AM   #4
Tool Geek
PaliBob's Avatar
Rewards Points: 2,160
Originally Posted by Bob Mariani View Post
................... GRC is needed in that case and PVC underground.
I Was not familiar with that acronym so I looked it up.
GRC is Galvanized Rigid Conduit
thanks
Also rigid is frequently run underground without transitioning to PVC.
Disclaimer
& Stay Safe
.....Bob Lavery
Old 01-29-2009, 11:00 AM   #5
thanks
Yes, but you should coat with a tar type paint for such uses. PVC is much better underground. Bur 12" minimum and cover with clean builder's sand.
Old 01-29-2009, 11:39 AM   #6
Electrical Contractor
PVC needs to be buried at least 18 inches.
You can be at the 12 inch minimum, if it's residential, 120 volts or less, max overcurrent device is 20 amp, and if it is GFCI protected.
hpp58 is offline   Reply With Quote