Old 12-20-2011, 09:05 PM   #16
Electrical Contractor
Electrical Wiring of Garage...Please Help
No and no!
It must be uf rated cable, or needs to be 4 induvidual conductors in pipe.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
jbfan is online now   Reply With Quote
Old 12-20-2011, 09:11 PM   #17
Licensed electrician
Originally Posted by cybex210 View Post
Also @ Jim what does it mean that I cannot parrallel conductors that small? You mean run those two cables along the same path so closely together?
I thought you were asking if you could run two smaller cables to equal a larger size cable. For example only, run 2 #10's instead of something like a #6.
If you install a subpanel at a detached building you will need a grounding system, like 2 8' rods.
The ability to run a 3 wire feeder to an outbuilding and re-bond the neutral and ground has been removed from the Code. Hence the need for 4 conductors.
Old 12-20-2011, 11:28 PM   #18
Electromagician
you've got the panel pretty well surrounded by 2x4s, so how will you get the wires into it?
I have a box of capacitors that can lower your power bill.
just ask me how.
powerfactor is offline   Reply With Quote
Old 12-21-2011, 02:30 AM   #19
Facilities Maintenance
I've noticed no ones mentioned it so I will.
NEC 210.8, states that all Electrical Recepticles in a Garage, Kitchen Counter, Bathroom, and outdoors must be GFCI protected.
Your building code may allow just having one GFCI Outlet, but having the rest run on the same circuit as the GFCI for a Garage, provided you label each recepticle with a sticker that states "GFCI Protected", OR, you may be locked in at requiring all outlets you install to be GFCI. You need to speak with your local cities commissioner office or city hall, and determine which is which, and what needs to happen.
Do not attempt to install unprotected recepticles in a garage.
GFCI Recepticles are a bit more expensive than regular outlets.
So it is important you figure out which applies to you.
Just putting that out there.
BigGuy01 is offline   Reply With Quote
Tags
breakers, electrical, garage, service panel, wiring diagram
low-voltage and electrical wiring sharing same stud space jheavner Electrical 21 10-06-2011 12:16 PM
Questions regarding wiring 220 to attached garage... John Green Electrical 0 01-20-2011 10:23 AM
Need some help with garage electrical issue Holt Electrical 25 06-21-2010 01:59 PM
Wiring project in my garage... Albatraz Electrical 4 05-20-2009 05:18 PM
Electrical problem in garage ginaca Electrical 10 04-19-2009 07:51 PM