Electrical Tester Reading HOT/GROUND REVERSE - Electrical - DIY Chatroom Home Improvement Forum
Old 07-30-2011, 12:55 AM   #1
Electrical Tester reading HOT/GROUND REVERSE
I have 3 outlets that are reading HOT/GROUND REVERSE on the tester and everything is wired up correctly. I can't figure it out. Can someone please help.
steelersdino58 is offline   Reply With Quote
Old 07-30-2011, 05:47 AM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,864
This is an indication of an open neutral somewhere on this circuit.
Could be in the panel, could be in one of the boxes.
Old 07-30-2011, 08:28 AM   #3
Electrician
SD515's Avatar
Rewards Points: 504
Are there other outlets on this circuit that test correctly? In addition to Speedy’s suggestion, could be in the last device box that is testing correctly. Also try tracing the circuit and look for junction boxes in the attic or basement that might have incorrect splices.
Kyle
Old 07-30-2011, 08:37 PM   #4
It's a double-wide, I posted on here earlier this week about an open service neutral. Come to find out, thats what the previous issue was. Tree branch popped the service neutral off at the transformer. That's fixed. Now there are 5 receptacles in this room. All tie in at the ceiling fixture. Don't ask. The light and switch work. The receptacle running the hot, comes back correct, 3 of 5 come back HOT/GROUND Reverse and 1 of 5 come back Open Neutral.???
Old 07-30-2011, 10:24 PM   #5
Electrical Contractor
kbsparky's Avatar
The one showing open neutral has no load on it.
The ones showing hot/ground reversed have a load applied on it, making the neutral appear "hot" and the subsequent false reading. You'll notice that your plug tester's instructions will tell you that it won't be able to discern more than one hot wire in the outlet.
With the neutral being "hot" due to the backfeeding from the applied loads, it fools the tester.
Probably a loose connection in that ceiling box.
-KB
How to install new electrical box without attic access gilmores33 Electrical 10 02-14-2010 08:46 PM
Electrical Engineer allowed to do Electrical work? SarahJennifer Electrical 48 09-21-2009 09:15 PM
Slight electrical current in bathroom faucet water + other unusual electrical events story Electrical 9 09-16-2009 11:28 PM
Electrical box replace,addiitions, city permits and looking for an electrician ramchy Electrical 3 08-02-2009 12:12 PM
Reverse Wiring (Hotwiring), Penny in Old Fuse Box rlmarr Electrical 14 03-28-2008 06:42 PM