I have an older home with an existing sub panel which is fused being fed by 3-wire. I would like to change it out to a circuit breaker sub panel but would like to know if I am able to run and external gound to the existing main panel, which feeds this. I am not able to ground conductor the in same raceway as the feeds to the sub panel. I would like the answer to be as per code. Thanks!
KellyElaine is offline   Reply With Quote
Old 01-17-2011, 03:39 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 470
Is the 3 wires that feed the panel now all insulated, or is one bare?
jbfan is online now   Reply With Quote
Old 01-17-2011, 03:41 PM   #3
It is all insulated.
Old 01-17-2011, 03:44 PM   #4
jbfan's Avatar
Rewards Points: 470
Is it conduit all the way to the main panel?
If it is, then it should be grounded.
Old 01-17-2011, 03:50 PM   #5
It is 6-wire MC or greefield. I don't think that is enough to be properly grounded. Also, all the circuits inside the panel are BX, no Romex
Old 01-17-2011, 04:05 PM   #6
jbfan's Avatar
Rewards Points: 470
What are using the other 3 wires for?
Are the wires paralleled?
Old 01-17-2011, 04:10 PM   #7
Two hots and a neutral. There is 220 volt through the wall heat pump on this sub panel as well as other single phase circuits.
Old 01-17-2011, 04:49 PM   #8
Rewards Points: 506
Raceway, BX, MC, Romex, single-phase circuits...
A lot of terms...
Why can't you use the existing 'raceway'?
jlmran is offline   Reply With Quote
Old 01-17-2011, 04:55 PM   #9
I can not get another wire in the existing raceway. Can I run an external ground to the main panel?
Old 01-17-2011, 04:58 PM   #10
Rewards Points: 506
For clarification, the sub is fed by 6 conductors?
Old 01-17-2011, 05:10 PM   #11
3 conductors - 6 wire - 60 amp fuse sub panel
Old 01-17-2011, 05:53 PM   #12
Rewards Points: 506
I'm lost. I'll stop chatting.
Old 01-17-2011, 05:57 PM   #13
Rewards Points: 506
Oh wait... You mean #6 wire...not 6 wires. Duh.
Old 01-17-2011, 05:59 PM   #14
#6 wire is correct
Old 01-17-2011, 06:09 PM   #15
iminaquagmire's Avatar
Rewards Points: 338
I think you mean you have 6-2 MC. This would have a black, a white, and a green ground. If this is the case, you cannot properly change out the panel and still meet code. You need to have another wire there. Now you say you have a neutral which confuses me. If you have 6-3 which is two blacks or a black and a red along with a white and a green ground, then you can change the panel as long as you keep the neutral and ground separate in the sub and don't bond the neutral bar to the panel housing. If you have BX (metallic sheath with bare silver bonding strip) with two phase conductors and a neutral, the armor can act as your ground back to the main panel. If you can run an external ground, you can run a new feed. That's the proper way. You also didn't mention whether this subpanel is in the main structure or a detached one such as a garage. That makes a difference how its wired as well.
iminaquagmire is offline   Reply With Quote
Sub panel wiring & grounding kwcamaro Electrical 1 03-06-2010 07:58 AM
grounding of main panel and sub panel in older house linkysys Electrical 2 10-01-2009 04:34 PM
new Main Panel Grounding lrr81765 Electrical 8 10-09-2008 11:16 AM
advice on installing equipment grounding bar in main panel pacifier1er Electrical 5 05-29-2007 05:55 PM