Old 09-21-2012, 07:09 AM   #1
I am thinking about upgrading my service panel from 100 amps to 200 amps. How do I tell what amperage my service wire can handle so i can determine if I need to upgrade it?
Chris
hullbo is offline   Reply With Quote
Old 09-21-2012, 07:46 AM   #2
Licensed electrician
Rewards Points: 1,892
Normally the ampacity of the service cable is the same as the main breaker rating. If larger cable is installed there is only increased cost, but no benefit.
Old 09-21-2012, 07:59 AM   #3
NEC Table 310-16 shows ampacity for copper and aluminum conductors. Here's a link: http://www.houwire.com/products/tech...cle310_16.html
Check the size of your service entry and see where it sits on the table. Don't forget to use the right temperature rating and check local code for things like ground and neutral size requirements (relative to the live conductors).
lynxpilot is offline   Reply With Quote
Old 09-21-2012, 08:34 AM   #4
PoleCat's Avatar
Rewards Points: 1,652
Your meter box will most likely need upgraded too.
PoleCat is offline   Reply With Quote
Old 09-21-2012, 03:09 PM   #5
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,992
If you now have a 100A service EVERYTHING from the connections at the top, down to the meter pan, the meter pan itself, service entrance cable, panel, grounding & bonding, MUST be replaced to upgrade to 200A.
New residential electrical service hounddog Electrical 6 12-05-2011 02:25 PM
Sharing Neutrals on the same phase electro Electrical 30 08-12-2010 02:10 PM
Ran a wire to an electrical panel for my first time Red Squirrel Electrical 17 07-19-2009 10:09 PM
Neutral Wire? 4x15mph Electrical 8 11-24-2008 01:00 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM